When the compressor starts it some times goes foward then goes backwards. Could the phase moniter change the direction for a few seconds. Anything on scroll would help.

Meer Abdulrehma
26-08-2009, 06:26 AM
am wondering how you can tell the direction of the compressor is it not sealed

nike123
26-08-2009, 09:24 AM
When the compressor starts it some times goes foward then goes backwards. Could the phase moniter change the direction for a few seconds. Anything on scroll would help.

Some models (without prevention of this occurrence) could go backwards only when power is cut off for short periods of time until pressures are equalized in compressor.

Check your motor contactor!

GHAZ
26-08-2009, 09:40 PM
scrolls have a internal non return valve which is a safety because when the compressor stops the discharge pressure does,nt back spin the scrolls ,it only spins back for a second ,until the pressures equilized, which is normal

littleyapper
28-08-2009, 01:33 PM
ghaz is spot on ...i know copeland have non return vlvs fitted but not too sure about other brands..

nike123
28-08-2009, 01:50 PM
ghaz is spot on ...i know copeland have non return vlvs fitted but not too sure about other brands..

Some older Maneurops where spinning backwards when de-energized.

IMSTIEN
01-09-2009, 12:02 AM
If it is not a millenium compressor, add a 5 minute time delay.

goshen
02-09-2009, 04:42 AM
When the compressor starts it some times goes foward then goes backwards. Could the phase moniter change the direction for a few seconds. Anything on scroll would help.
hi there a phase monitor is as only a monitor and will not cause a phase change only monitor it and warn u or stop your system when needed
u should go to the copeland site or maneroupe they have a nice "show " and explanation how a scroll works.
http://www.digitalscroll.com/sb300/
enjoy:)