19-08-2009, 03:34 PM
Can this be done and has anyone done it ?
PM me if required ;)


Ok Outside MHI Multi SCM80ZGS

i have a customer who has 4 class rooms
He cant use all of the 4 class rooms at the same time.

So a 80 outside unit with 2x63 and 2x35 wall units work just right with just 2 being used at the same time. So that's 4 wall units on to the 80 outside.

Will they work / talk with the outside unit.
Or will there be errors, saying - hey you cant have 2x63 and 2x35 on the same unit. ?

Trying to save the customer money, and get the job myself in the process ;)

taz24
19-08-2009, 11:22 PM
Can this be done and has anyone done it ?
PM me if required ;)


Ok Outside MHI Multi SCM80ZGS

i have a customer who has 4 class rooms
He cant use all of the 4 class rooms at the same time.

So a 80 outside unit with 2x63 and 2x35 wall units work just right with just 2 being used at the same time. So that's 4 wall units on to the 80 outside.

Will they work / talk with the outside unit.
Or will there be errors, saying - hey you cant have 2x63 and 2x35 on the same unit. ?

Trying to save the customer money, and get the job myself in the process ;)

http://www.ivik.ua/equipment/aircons/mhi/srk/2007/multi/images/6.gif

Outdoor unit specificationshttp://www.ivik.ua/images/spacer.gifhttp://www.ivik.ua/images/spacer.gif

SSCM80ZG


Indoor unit total capacity is 13.5 Kw

Your combinatin is over 19Kw and the Mitsi will be over indexed and will not allow you to do it.
It will allow a maximum of 13.5 so if you could reconfig the indoor units then you could do that.

Have you thought about the Samsung range. They can be configed upto 170% of the outdoor unit.


taz.

.

S_Line
20-08-2009, 11:18 AM
Thanks for the reply,
HRP have just started selling Sammys,
We have installed a Demo one in our office.
Only problem is, HRP havent sent us any info on the Sammy range yet.
So cant speck up a Sammy multi at the moment.