View Full Version : TXV query



amitsaxena
11-08-2009, 06:45 AM
Dear All,

I have two identical system, the only diffenece i am finding is the TXV, as

Following are the observations,

1. The Suction temp. and pressure are higher as

System #1 System #2

20°C 28°C

2. The Eva. temperature is also on the high side as

System #1 System #2

3°C 10°C

Rest all parameters are same in both the systems


Can you suggest what all possibilities are there?

Thanks
Amit Saxena

Gary
11-08-2009, 06:56 AM
Very likely there is less airflow through the condenser in system #2.

What are the entering and leaving air temps on both systems?

amitsaxena
11-08-2009, 07:21 AM
Dear Mr Gary,

The entering and leaving air temps are as

System #1 System #2
Air In 42°C 42.1°C
Air Out 49.5°C 51.2°C

Thanks
Amit

lowcool
11-08-2009, 09:50 AM
is the heat load a bit lower in one room?