View Full Version : Scotsman ACM225 on high condenser temperature



hyndovich
08-08-2009, 12:27 PM
Hi,

I have been back and forward to this ice machine a few times now and have ran out of ideas on why it keeps tripping off.
The original problem I found was a lack of water in the sump causing the machine to run dry by the second or third batch. I removed the inlet valve, cleaned the filter and replaced the fill hose which appeared to solve the problem.
Now the machine will run for a few days to a week then trip off on high condenser temp fault.

The condenser is clear and fan is running
The refrigerant charge is fine
The The coil is freezing all over

hyndovich
08-08-2009, 02:42 PM
Hi,

I have been back and forward to this ice machine a few times now and have ran out of ideas on why it keeps tripping off.
The original problem I found was a lack of water in the sump causing the machine to run dry by the second or third batch. I removed the inlet valve, cleaned the filter and replaced the fill hose which appeared to solve the problem.
Now the machine will run for a few days to a week then trip off on high condenser temp fault.

The condenser is clear and fan is running
The refrigerant charge is fine
The coil is freezing all over

Any advice would be appreciated

Thanks

Frikkie
08-08-2009, 04:30 PM
Can you say for everyone what gas is it using? What is low and high side pressures?

Thank you.

Yuri B.
08-08-2009, 06:28 PM
However, I have not worked for a long time on ice machines, does the fan goes on on the command from a sensor in the condenser?

nike123
08-08-2009, 06:39 PM
Hi,

I have been back and forward to this ice machine a few times now and have ran out of ideas on why it keeps tripping off.
The original problem I found was a lack of water in the sump causing the machine to run dry by the second or third batch. I removed the inlet valve, cleaned the filter and replaced the fill hose which appeared to solve the problem.
Now the machine will run for a few days to a week then trip off on high condenser temp fault.

The condenser is clear and fan is running
The refrigerant charge is fine
The coil is freezing all over

Any advice would be appreciated

Thanks

What is condenser air on and off temperature?
What is subcooling and superheat?
What are saturation evaporation and condensation temperatures?
What is ambient temperature where ice maker is placed?

philfridge
08-08-2009, 06:54 PM
Is ventilation adequate all the time ?

mcunliffe4
08-08-2009, 07:18 PM
could have intermitent fault with probe

philfridge
08-08-2009, 07:24 PM
Water inlet solenoid faulty

nike123
08-08-2009, 07:33 PM
Water inlet solenoid faulty
What is that got to do with high pressure error on air cooled condenser?

nike123
08-08-2009, 07:35 PM
NOTE. In case the condenser temperature
probe senses that the condenser temperature
has rised to 70°C (160°F) - on air cooled
versions - or 62°C (145°F) - on water cooled
versions - for one of the following reasons:
CLOGGED CONDENSER (Air cooled
version)
INSUFFICIENT FLOW OF COOLING
WATER (Water cooled version)
FAN MOTOR OUT OF OPERATION (Air
cooled version)
AMBIENT TEMPERATURE HIGHER THEN
40°C (100°F)
it causes the total and immediate SHUT-OFF
of the machine in order to prevent the unit
from operating in abnormal and dangerous
conditions.
When the ice maker stops on account of this
protective device, there is a simultaneous
glowing of the RED LED, warning the user of
the Hi Temperature situation.
After having eliminated the source of the
condenser hi-temperature, to restart the
machine it is necessary first to rotate for a
while the program selector on RE-SET
position then again on OPERATION position
or to unplug (wait few seconds) and plug in
again the unit. The ice machine resumes its
normal operation by going through the 5
minutes water filling phase.

http://www.scotsice.com.au/mainsite/Service%20Manuals/Scotsman/07%20AC%2085-225%20-%20REV%2001-2001.pdf (http://www.scotsice.com.au/.../)

philfridge
08-08-2009, 08:08 PM
What is that got to do with high pressure error on air cooled condenser?

Original fault was insufficent water supply, so we have to go with that first. Now it is highly likely that this solenoid
Could now be' letting by 'allowing 'warm' water to continually enter the machine causing a high temperature cutout.