:eek: I am a qualified assesor and lecturer in refrigeration and am qualified to assess amongst other things City and Guilds 2079 safe handling of refrigerants and Citb equivalant. I am concerned that engineers are telling me that when recovering refrigerants that they are using manafacturers fill quantities that are stamped on cylinder bodies.

BSEN 308 2008 state that bottles must only be filled to 70% of this the old bsen378 was 60%. Recovery bottle suppliers are giving wrong advise if they state different. If you hold City and guilds 2078 or equivalent including 2079 you should already be aware of this.

please take care

littleyapper
31-07-2009, 01:37 PM
fair play.... ever thought about comming to ireland to do the 2079

weatherman
31-07-2009, 01:44 PM
I know someone who goes to treland regularly training

Peter_1
31-07-2009, 06:13 PM
EN378/2008 says 80% :confused: I'm a Belgium assessor

Peter_1
31-07-2009, 06:15 PM
There was a discussion on this forum regarding F-Gas questions which aren't correct or interpreted different ways. Are you ware of this.

weatherman
11-08-2009, 09:48 PM
EN378/2008 says 80% :confused: I'm a Belgium assessor
Correct my mistake. Some 2078 trainers are still quoting 60%. The point i was making was that some recovery cylinder suppliers are not aware and are giving out wrong advise when questioned