Was hoping some of you gurus could help me out with trouble shooting my chigo mini split ac that I've installed.
After installing unit ran great for about 18 hours, then threw up an error code of "e4". If you turn system off then back on again, it will run good for about 30 minute then error code pops up every time.
So, after doing extensive research on these units through forums and other means of information I've come up short. The only thing I have found is this which is from the manufacturers website:
If unit displays "e4"
1、 Check whether the winding resistance and
operation current of the compressor are normal.
2、Check whether the high and low pressure is normal
when the unit is running.
3、Check (whether the coil pipe sensor is normal)
whether the contact of the inserter on the circuit
board is well, the coil pipe temperature sensor is
fixed, the evaporation of the indoor unit is well,
the key is to check the evaporator temperature
detected by the coil pipe temperature sensor has
reached the cooling or heating temperature.
4、Check whether the surface of the condenser is too
dirty, it should be cleaned when it is too dirty.
5、Check whether the capacitance of the outdoor motor
and the fan is damaged, it should be replaced when
it is damaged.
6、If the above items are normal, the electric control
board should be replaced.
Ok, after contacting manufacturer tech, he ensured me that #6 would be the problem so he sent me a new electronic box as well as a new capacitor. After replacing both the unit still shows "e4". My thinking is that this cancels out #5 and #6, also the unit is brand new and spotless so I think that also cancels out #4. If my thinking on these three not being the problem is incorrect please let me know.
So, this leaves us with #1, #2, and #3. Unfortunately I'm a novice but feel capable of checking these three with a little help.
Any help or comments would be greatly appreciated, and if pictures will help I would gladly post some.
Thank you.
After installing unit ran great for about 18 hours, then threw up an error code of "e4". If you turn system off then back on again, it will run good for about 30 minute then error code pops up every time.
So, after doing extensive research on these units through forums and other means of information I've come up short. The only thing I have found is this which is from the manufacturers website:
If unit displays "e4"
1、 Check whether the winding resistance and
operation current of the compressor are normal.
2、Check whether the high and low pressure is normal
when the unit is running.
3、Check (whether the coil pipe sensor is normal)
whether the contact of the inserter on the circuit
board is well, the coil pipe temperature sensor is
fixed, the evaporation of the indoor unit is well,
the key is to check the evaporator temperature
detected by the coil pipe temperature sensor has
reached the cooling or heating temperature.
4、Check whether the surface of the condenser is too
dirty, it should be cleaned when it is too dirty.
5、Check whether the capacitance of the outdoor motor
and the fan is damaged, it should be replaced when
it is damaged.
6、If the above items are normal, the electric control
board should be replaced.
Ok, after contacting manufacturer tech, he ensured me that #6 would be the problem so he sent me a new electronic box as well as a new capacitor. After replacing both the unit still shows "e4". My thinking is that this cancels out #5 and #6, also the unit is brand new and spotless so I think that also cancels out #4. If my thinking on these three not being the problem is incorrect please let me know.
So, this leaves us with #1, #2, and #3. Unfortunately I'm a novice but feel capable of checking these three with a little help.
Any help or comments would be greatly appreciated, and if pictures will help I would gladly post some.