Hello Everyone,
I got a problem hear with a three freezers and two fridges connected to a bitzer compressor, the fridges are running on the nomal temperature, but the freezer seemse quart different running below the nomal setting temperature. and the suction pressure is below.
What can I do to solve this????

homelover
19-08-2004, 08:17 PM
To give advice to any problem we need all the running pressures and temperatures,
Plus which refrigerant is being used, how the system is piped and what control system is used.

Is the a capacity control system on the unit and what size is the compressor.
The more information supplied the easier it is to help you.
Homelover

chemi-cool
19-08-2004, 08:37 PM
Hi Raleighe.

If you didnt change any settings and defrost is ok.
check refrigerant charge and look for leaks.
Thats only to start with.

Chemi

master rinktec
07-09-2004, 04:46 AM
What do these evaporators have for pressure regluation? EPR's? I also agree the charge is worth checking out. One other thing that could cause the symptoms is plugged suction filters if there are any. Hope this helps.