i am looking to power and wire up a lossany hrv and was wondering, do i have to get seperate control for this or can i tap off an excisting mitsu controller belonging to a vrf system with a g50 central control ???

rgrds phil

Thermatech
18-07-2009, 12:56 PM
Yes can control using G50 / AG150

Make Mnet 30v dc wiring on daisy chain with any other indoor units.

Make sure the Lossnay address is after all the indoor units.

For example
If you have indoor units 001 up to 045
then make Lossney address 046 up to 050.

When you program the G50 you can make each loosney a group & control the same as any other indoor unit & make any time clock shedule for each loosney that you feel appropriate.

You also have the option to interlock so that when any indoor unit is turned on the lossney automatically comes on also.

philjd26
18-07-2009, 02:07 PM
thanks thermatech,
so..i will connect the lossnay on the m net, and this will automatically picked up by the g50 once the addresses are correct, the only thing i wil have to do is edit the name of unit maybe???
i just wanna get thing running on the same schedule as indoors thats it..

rgrds phil

Thermatech
18-07-2009, 05:01 PM
Thats it

Give the Lossnay an address the same as you would any indoor unit.

Dial that address in for a group at the G50 the same as you would to set up any indoor unit at the G50.

Give the Lossnay group the same time clock schedule you give to all the indoor unit groups.