View Full Version : scotsman acm125 fault



skeggyboy
08-07-2009, 08:59 PM
can anyone help.i have a scotsman acm125 ase 06uk.unit runs for a short while then shows fault too hot.have checked refrigerant,cond and fan and all are ok.any suggestions

Grizzly
08-07-2009, 10:35 PM
Welcome skeggyboy.

May I suggest you look at your evap sensor?

The below link may help.

http://www.mediafire.com/?sharekey=06e4e1cf4e37bb5d19747bd91027d4dd8c7f7500a159d902


Good luck Grizzly

Gary
08-07-2009, 10:38 PM
What is the temperature of the air entering the condenser?

What is the temperature of the air leaving the condenser?

philfridge
09-07-2009, 09:37 PM
You will need to check the Evaporator coil is reaching -15c within 20 minutes or unit will not work. Could be a faulty coil sensor as grizzly says but you should first rule out refrigeration problem with coil temperature not being achieved in time.

sparkout
09-07-2009, 10:01 PM
HI Grizzly

Many thanks for the link for the manual.

sparkout

mcunliffe4
11-07-2009, 07:50 PM
had this problem otherday on a water cooled cond, site had turned of water inlet to cond. machine would start up, run a couple of minutes untill probe in cond coil got to hot, help this helps

skeggyboy
15-07-2009, 06:23 PM
thankyou very much for your reply.replaced faulty evap sensor and all working fine.thanks