View Full Version : goodman Cpkj60-1c Reversing valve



mastercheif602
07-07-2009, 06:10 AM
I had my dad ac go out this weekend. The tansformer was burnt out. Replaced it and then started the unit. It is a Five ton heat pump. The unit would not go into cool as the valve would not move over. Then I smelled burning. The tansformer was getting hot, then the unit stopped. I let it cool down and went out side to check the uint. It came back on when I removed the power to the coil on the reversing valve. Has any one had the coil on the valve take out a tanformer. :eek: The Tansformer is 40 va big enought for this unit.

lowcool
07-07-2009, 12:39 PM
thats what happens when it is not protected by fuses,your transformer out put is like your power supply but it is protected i hope by the like

mastercheif602
07-07-2009, 02:53 PM
it is fused on the incoming power only. But you have seen that happen?

lowcool
08-07-2009, 01:11 AM
no different than 240v on primary 240v on secondary used say as an isolation transformer running fan motors. yes i have seen it had to replace a $350 tranny because $2 inline fuse was not fitted to fan motor wiring.

mastercheif602
08-07-2009, 03:42 AM
Just making sure. Thank you:o

mastercheif602
15-07-2009, 01:54 AM
changed it this weekend and it worked not more tans
former melt down.:D

lowcool
15-07-2009, 02:58 PM
hope you protected the trans