View Full Version : Toshiba Air Conditioning fault codes,
suctionheader
04-07-2009, 01:50 PM
Does anybody know what these codes are ?
01 06 and 1E are the ones that have been showing at a site I have been working at.
Grizzly
04-07-2009, 03:22 PM
Hi suctionheader .
Download from the link I have provided and the codes are explained.
Good Luck Grizzly
http://www.mediafire.com/?sharekey=06e4e1cf4e37bb5d19747bd91027d4ddd2b07cc7f7a4c543
Not all the codes you state are there though.
What is the actual unit you have a problem with?
frank
04-07-2009, 03:33 PM
Follow this link
http://www.realtime-controls.co.uk/products/Toshiba%20Fault%20Codes%20LTX-21%20iss2.00.00.pdf
The first part of the code is the unit number, the second (06) relates to how many times the electronics have tried before finally giving up and the last part is the actual error - in this case, High Dischage pressure
Loops
14-07-2009, 10:02 AM
Hi Suctionheader,
Sorry Frank you are wrong. There is no count for electronics trying to start then giving up. (but some models have a compressor start count)
I think the codes should read
01.0b
01.1E
The 01 is the master unit
06 is actually 0b and is a float switch trip - check drains \ pump operation.
1E is the compressor discharge temerature exceeded 130C - check air flows (in & out), gas charge & Td sensor.
Hope this helps
Loops
Latte
14-07-2009, 07:50 PM
http://www.refrigeration-engineer.com/forums/showthread.php?t=16639
Regards
Latte
Argus
14-07-2009, 08:29 PM
.
............ Listen to what Loops says, he knows the kit inside out.
.
paddyaircon
25-08-2009, 09:04 PM
does it matter what order you wire the p q wiring in a multi modular 407c?
Loops
28-08-2009, 09:25 AM
Paddyaircon,
I'd sugest you should have started a new thread for this enquirey but seeing as you've asked a question........
The PQ network on the old R407c 2-pipe modular multi is a non-polarised network. Just wire from one end to the other (not ring main style).
You'll need a 1.5mm2 2-core screened cable minimum.
Cheers
Loops
S_Line
29-09-2009, 03:21 PM
Just had a call from one of our engineers and hes got P10 code up on the controller.
Its a RAV unit,
I told him to ring Toshiba Technical, as P10 isnt listed :lol:
P10 is "Float switch open circuit (high water level)"
Cheers
Eggs
Latte
01-11-2009, 04:27 PM
Thanks Egg,
I have just come back from another call with that fault and after going through all my Tosh books i couldnt find anything either. Had booked it to go back after speaking to Toshiba but thats saved me a phone call
Regards
Latte
Powered by vBulletin® Version 4.2.1 Copyright © 2024 vBulletin Solutions, Inc. All rights reserved.