unit
fujitsu inverter

indoor model:ABTA45LAT(UNDERCEILING CASSETTE)
out door model:AOTA45LATL

problem: bth indoor and outdoor unit nt running
indoor lights all off
my diagnosis
OUTDOOR UNIT
checked voltage on outdoor ,L-N =240V
checked voltage N-1=240V
CHECKED VOLTAGE 1-2=240V

disconnected 3 from terminal block and checked voltage, 2-3=90v-125v
checked voltage, 2 and the disconnected 3 which goes to indoor got 84v

INDOOR UNIT
CHECKED 1-2 =240V
CHECKED 2-3=30V-90V

TO CHECK
COMPRESSOR MOTOR WNDINGS RESISTANCE
BTH FAN MOTORS WINDING RESISTANCE



Any input welcome thank you

nike123
02-07-2009, 05:26 PM
What kind of remote controler you got.

Check Fuse in Filter PCB.
>> If Fuse is open, check if the wiring between Terminal and Filter PCB
is loose, and replace Fuse.

Check Varistor in Filter PCB.
>> If Varistor is defective, there is a possibility of an abnormal power supply.
Check the correct power supply and replace Varistor.

bangoman
02-07-2009, 10:18 PM
Nike 123 ,The remote controller is a wireless hand held one .

paul_h
03-07-2009, 10:58 AM
Dumb question, but you've tried pushing the auto button on the indoor unit to make sure it isn't a remote control or reciever problem?

Is this a DOA unit or has it worked before?


edit: are you sober yet nike? Have you had a look at that PM i sent?