View Full Version : Hitachi RAS20 problem



TRASH101
01-07-2009, 11:46 AM
Hello chaps

Does anyone know under what condition the fixed speed condensor fan is supposed to be enabled?

Thanks very much.

Thermatech
01-07-2009, 03:17 PM
The outdoor unit has target discharge pressure of 23 to 27 bar in cooling mode & uses both fixed & inverter fan to maintain the target pressure.

The fan motors have built in over heat thermostat.

So if the fixed speed fan not running
suggest look at operation of the internal stat or the high pressure sensor.
If the high pressure sensor is providing incorrect data for very low discharge pressure then the fan could be off.
So compare the high pressure data on the 7 segment display with your hp gauge reading.

TRASH101
02-07-2009, 08:34 AM
cheers for your response TTech

I worked it out eventually. From what I can gather it uses a step method (0-16) where the variable speed fan controls by itself from 0-11. The step is controlled by target pressure.

Thanks again