View Full Version : Remote condenser



plnac
24-06-2009, 10:05 AM
I am looking into re locating a copeland mc-r7-zf33ke condensing unit. Because of its current position this will be very difficult.

It would be much easier to remove and re install the condenser remotly.

What things should i consider when doing this?

The pipe run is 10m at the moment but the condenser will be a further 10m awy with a 3m rise.

Kh1971
24-06-2009, 10:11 AM
Hi,

I do change the location of the condenser before but not that far, i think you have to check the pipe size first, second the oil traps, and you have to fix very well the condenser in the new posiiton

D.D.KORANNE
24-06-2009, 12:19 PM
Receiver warm up in plant room could make it difficult for liquid drain to receiver , a vent line from receiver to condenser would be of help .