hello, i have a cps vg200 digital vacuum gauge and the readings are up the creek, it will only read properly if not connected to system. once the system is in a vacuum it just takes a lon time to register what micron it is reading. has anyone else seen or heard of this. thanks CT

kiwireeferman
22-06-2009, 12:31 PM
Have you tried washing the sensor in alcohol or similar. May be oil contaminated.

Brian_UK
22-06-2009, 11:39 PM
Are you sure that the vacuum you have created is low enough to register on the gauge?

Also, as stated above, make sure that the sensor is clean and the battery is good.

cool_tech
24-06-2009, 08:57 AM
hey guys
cleaned out with metho pulled vac pump down to 250 microns with dirty vac oil in pump.
thanks for your help guys

sidi
25-06-2009, 08:18 AM
Hi, guys
Can anyone tell where I can buy pressure gauges, vacuum pump, recovery unit,..etc.. but not too expensive for a tight budget and somewhere here in London.
Thanks

cool_tech
25-06-2009, 08:58 AM
local refrigeration dealer, i paid $330 aud for the vac gauge, $460 for a 120l/min vac pump. recovery unit about $900 aud. which is pretty good price for all

chillifive
30-06-2009, 12:53 PM
Hi, guys
Can anyone tell where I can buy pressure gauges, vacuum pump, recovery unit,..etc.. but not too expensive for a tight budget and somewhere here in London.
Thanks


try ebay mate, may even be cheaper from o/seas with ur exchangerate
shaun

FreezerGeezer
30-06-2009, 01:37 PM
Ah ha, another G.C-er! Welcome to R-E chillifive. :)

Sidi, I'd try fleabay. However remember you get what you pay for!

icecube51
01-07-2009, 08:05 PM
in Belgium we have a saying " goedkoop is niet altijd goeiekoop"...so translated it sounds " cheap bying isn't always best bying"

Ice

ICE/RUNNER
01-07-2009, 08:17 PM
Had the same problem myself, connected up the vac pump and stared pulling a vac, next the gauge stops working. Vac pump had pulled out oil mist from the system and contaminated the sensor. Now i vac systems for an hour befor fitting the guage, no more failures.

ice/ruuner

Brian_UK
01-07-2009, 10:47 PM
^ Also, vac guage shouldn't be fitted to vac pump; it should be connected directly to the system if possible.

FreezerGeezer
03-07-2009, 01:18 AM
And also as far on the system from the vac pump connection as you can get.