View Full Version : chiller unloading



jebar
18-06-2009, 04:17 PM
hi all I have chiller type ALRHAST455.4 the chiller is controled by microtech (McQUAY) when the chiller start normaly & then the comp. loading is 100% the water temp. 34c the temp. setting is 10c.
any advice please.

Grizzly
18-06-2009, 05:44 PM
Your LP and HP settings are?
liquid line temp etc etc.
Give us some details so we can help you jebar!
Grizzly

icecube51
18-06-2009, 09:33 PM
what is infact yore question??

Ice

shiyam
04-04-2011, 11:09 AM
hi all I have chiller type ALRHAST455.4 the chiller is controled by microtech (McQUAY) when the chiller start normaly & then the comp. loading is 100% the water temp. 34c the temp. setting is 10c.
any advice please.
===reply shiyam from uae} you did not write 34 c, leaving or return water( temp)clearly. so when the leaving water temperature 34c better one more chiller. so you should understand and lean unloading loading chilled water temperature point.
thank you
shiyam...(mshiyam88@yahoo.com (mshiyam88@yahoo.com))

stufus
04-04-2011, 06:42 PM
As others have stated your post is not clear .
If you are saying when your chiller starts the water circuit temperature is 34c and the chiller set point is 10c, whether it is leaving or return water temperature is irrelevant as either way you are 24c above set point.
At 24c above set point i would expect the loading to be 100%
You need to clarify your post and give us more information .
Cheers
Stu

Magoo
05-04-2011, 12:23 AM
A really old post.
But generally chiller are controlled on return water temp., so set point +10'C , split 5.5'C leaving water at +4.5 'C .

yorkman_gr
18-04-2011, 07:33 PM
and of course this 5.5C ΔΤ depends on the pressure drop across the evaporator DP