16-06-2009, 11:04 AM
Hi all could any one help regarding the above the chiller keep s coming up with starter gaurd alarm,
The chiller cycles alot due to poor load, i think this is a antirecycle protection is this correct???
thanks
mariobros
Brian_UK
16-06-2009, 11:31 PM
Can't find any reference to 'Starter Guard' in the manuals, what is the alarm code?
Manual here if you want one....
http://eto.carrier.com/lit.asp
select 30HG and 'all'
vinod
17-06-2009, 04:34 PM
Hi,
Check your cc heater
icecube51
21-06-2009, 11:25 AM
did you do any mesurments at all ???
presure - temps - time - etc.ect.. ?
Ice
Brian_UK
21-06-2009, 11:24 PM
Are we going to hear from him again ? ;)
goshen
24-06-2009, 06:59 PM
as mentioned before check your oil heater .the start guard monitores this
if all else failes switch a startguard card from a near compressor .to verify its operation and if needed buy a new one it is not that expensive
in order to reset a start guard .u need to turn off the power supply to the start guard
this is only if u messured your currents and compressor parameters and found all ok
nh3wizard
24-06-2009, 07:06 PM
I doubt it, just another 1 post wonder
thebigcheese
24-06-2009, 10:19 PM
crank heater or sensor fault
Mariobros
30-06-2009, 06:27 PM
Thanks all sorry for no reply dont get on here much got some good info from link posted
Have a good week all