13-06-2009, 12:31 AM
Hi
Many times I faced the same problem but I havent got
an accurate answer .It relates with a rotary or piston compressor
that draws more than the required power till its internal
overload opens ,I know that a defective capacitor could lead to this but I am talking when the capacitor is
not defective and the condenser is clean also the fan is
working properly ,most of technicans consider it a coil
problem an I agree with them ,hence when checking the
coil for ground how much the reading should be ?Personally I reached above 40 MOhm and no ground ,other than that I have to assume a small contact between the start an running coils.The last assumption is a refrigerant contamination .
Please anyone have more about that I will be thankful
Here are some information about the case:
- The unit is R22 ( although I experienced the same problem with R 12 and R 134 a ).
- For R22 suction presure is 55-60 psi and the outdoor temp. is 80 F .Indoor entering dry bulb temp
is 82 F.
- The unit starts normaly but after about 10-15 min. the amperage begins to rise gradually until
the internal overload opens.
- No earth between the terminals and the body exists below 40 Mohm.
* For me the 2 Mohm is very small and any compressor that have such resistance as an earth
will not work properly .
-
Many times I faced the same problem but I havent got
an accurate answer .It relates with a rotary or piston compressor
that draws more than the required power till its internal
overload opens ,I know that a defective capacitor could lead to this but I am talking when the capacitor is
not defective and the condenser is clean also the fan is
working properly ,most of technicans consider it a coil
problem an I agree with them ,hence when checking the
coil for ground how much the reading should be ?Personally I reached above 40 MOhm and no ground ,other than that I have to assume a small contact between the start an running coils.The last assumption is a refrigerant contamination .
Please anyone have more about that I will be thankful
Here are some information about the case:
- The unit is R22 ( although I experienced the same problem with R 12 and R 134 a ).
- For R22 suction presure is 55-60 psi and the outdoor temp. is 80 F .Indoor entering dry bulb temp
is 82 F.
- The unit starts normaly but after about 10-15 min. the amperage begins to rise gradually until
the internal overload opens.
- No earth between the terminals and the body exists below 40 Mohm.
* For me the 2 Mohm is very small and any compressor that have such resistance as an earth
will not work properly .
-