View Full Version : General Cassette Fuse Problem



Cool Mike
07-06-2009, 11:32 AM
Hi All,

I have a 26 000btu General ceiling cassette heat pump type unit. The fuse on the outdoor unit keeps fusing. If I disconnect the compressor from the relay, it works fine, the relay switches without a problem. If I run the compressor on its own it also works fine. As soon as I connect the compressor up it will sometimes pop the fuse on start up. Any ideas?

Help will be greatly appreciated.

fazzamouse
07-06-2009, 12:09 PM
breaker type and rating?

brunstar
07-06-2009, 01:11 PM
make sure that your cables resistance is ok as you may have either a faulty cable going to your contactor coil.
also check the resistance of your contactor coil.

nike123
07-06-2009, 01:52 PM
What is model #?

Yuri B.
07-06-2009, 03:40 PM
I suggest the micro-relay's contacts on PCB are worn out - and at some times, when you are away, compressor's contactor, fed through that relay on PCB , begins frantically switching on and out. The fuse of the L to cassete blows out.