PDA

View Full Version : DORIN Comporessor Info Needed



MikeySq
04-06-2009, 12:52 PM
Hi I was wondering if anyone had dealt with an Italian Gelato case. I have a siezed compressor drawing LRA. The compressor is a Semi Hermetic pump kind of the same size as a Copeland K-Body. I don't think I'm going to get a direct replacement with the time and cost issues I have to deal with. I need the info on the OEM pump to get the capacity in order to know what Copeland to cross reference it to.

I'm In Canada so Dorin compressors are not readily available.

Compressor INFO:
Make _ DORIN
M# H180CS/FB-UL
S# 04070494C
Thermal Protection PTC
208/230V/3/60, 9,7/9.2A
1.8HP 1750RPM UL SA 11929
R-404a
Oil POE 32 KGI
Manufactures by Officnje Mario
Dorin, Italy

I don't have the make/Model info for the case it was worn off.

if it's familiar does anyone know the little controller program? It looks as it may be similar to a lil Dixell controller maybe.

TIA
Mike

Grizzly
04-06-2009, 04:53 PM
Welcome Mikey.
Below I have pasted the comp details direct from the Dorin site.
Hopefully this will help you or someone else to identify a replacement.
Grizzly

H180CS
8,47 m3/h ; 1,8 hp
Mass Flow 50Hz
8,47
m3/h
Mass Flow 60Hz
10,16
m3/h
n° Cylinders
2

Bore
44
mm
Stroke
32
mm
Standard Power Supply


220-240V(delta)-380-420(Y)/3/50
RLA (400V 50Hz)
20,0
A
FLA (400V 50Hz)
4,4
A
RLA (400V 60Hz)
24,0
A
FLA (400V 60Hz)
5,3
A
Service Suction Valve
16s

Service Discharge valve
12s

Net Weight
39
kg
Oil Charge
1
kg
Oil Type (with HFC)
POE 32
cSt
Oil Type (with R22)
minerale 32
cSt
Max Operating Pressure
22LP / 30,5HP
barg
Eletrical box insulation
IP55

Crankcase Heater
optional

Unload Start
/

Head Fan
optional

Capacity Control
/

Water Cooled Head
optional

Liquid Injection (D.T.C.)
/

Oil Pressure Control (D.P.S.)
/

Vibrational Dampers
Standard Equipement

chemi-cool
04-06-2009, 06:57 PM
You can download from Dorin website all the info you want + a compressor selection software.

D.D.KORANNE
16-11-2009, 09:37 AM
Easy way out to workout for a replacement model is to select a compressor based on meter cub per hour displacement .

D.D.KORANNE
16-11-2009, 09:57 AM
Try alternate brands !

tonyelian
16-11-2009, 07:30 PM
hi
ur compressor can provide 2583 watt@-25degree centigrade
the alternative one is copeland
eava-020etav it can provide2635 watt@-25 hope that help

lowcool
17-11-2009, 11:25 AM
whats the tx valve capacity?and its morethan likely an eliwell controller if over a couple of years old