View Full Version : Control Panel
This is a pic from a Copeland Semi 8Hp control panel.
I need to identify certain components........ie: 3 phase protection , etc
From the pic can any members identify??
chemi-cool
21-06-2004, 07:10 PM
Hi Abe.
QSG is main isolator.
QM1 is compressor overload
KM1 is compressor contactor
QM2 is fan overload
KM2 is fan contactor
QM7 is "0" protector
KT1 is a timer most probably short cycle protection
KA2 is a control relay and so is the other.
the control box is not connected to the mains, why?
Thats what I can see from here :D (4500KM away)
Does it help?
Chemi
Hi Chem,
You did a brilliant job analysing the photo, from far away. !!!
I need to take in what youve put down............
How did you manage to read the stuff on the devices???
You must have eyes like an eagle !!
The system is not connected.......
I disconnected it, the compressor is not working,
You would make a very good sleuth.........( detective !!! )
lol
Now on the existing set up, if I lost a phase, would QM1 trip and shut the compressor down??
I think Im confused between what a phase protection device is and what a overload device is
Are the both the same? Can they both do the same job?
chemi-cool
21-06-2004, 08:32 PM
My eyes are not so good but my reading glasses are as thick as a Coca-Cola glass bottle's bottom. :D
Its prety clear Abe.
If you want to add a phase sequence protector, connect it after the main isolator and from the QM7 take the "0" through the NC contacts.
That should do the job.
Forgot to mention, I use photoshop to play with the picture ;)
Chemi
chemi-cool
21-06-2004, 08:45 PM
Hi Abe.
I've sent you a pdf showing a phase sequnce data sheet.
Too big to post her.
Chemi