View Full Version : single phase 208v



j.a.violante
24-05-2009, 12:10 AM
good memorial day weekend to all,
question:
on a single phase 208 volt a/c compressor (Tecumseh)
i am not finding any relay to drop out the start winding
as is the case with a typical 115v slit phase compressor.
It is a CSR motor with one cap.Is a centrif.switch living
inside the hermetic???
I have experience with split phase and three phase
but need some help with the above. thanks!
Best Regards

Yuri B.
24-05-2009, 06:37 AM
Wikipedia:
A variation of the centrifugal switch used a changeover contact to ensure that the auxiliary windings remain in the circuit through a running capacitor. These motors are called two-value or capacitor start capacitor run motors (http://en.wikipedia.org/wiki/AC_motor#Capacitor_start_motor).

Yuri B.
24-05-2009, 07:18 AM
Your motor is evidently capacitor start and run. One and the same cap ensures both the start and the run phase shift.