View Full Version : Water dripping continuously for Split AC
amitsaxena
14-05-2009, 05:58 AM
There is continuous water dripping from my Split AC. What may be the possible causes?
Please suggest.
Thanks
Amit
nike123
14-05-2009, 06:41 AM
Describe where is dripping ?
Yuri B.
14-05-2009, 08:54 AM
Condensation pump, if installed, out of order.
Dirt in pipe (too dirty air in the room), or pipe sqweezed on a bending, canalization where the pipe goes in is stopped.
Pipe diameter too thin for the load - too much condensation is being produced.
Much condensation, but unit installed not horizontally (water spills over one of its brinks).
amitsaxena
14-05-2009, 09:23 AM
Mr. Nike,
Water is continuously dripping from the front grill and Coil is fully frosted.
thanks
amit
Yuri B.
14-05-2009, 09:59 AM
Amitsaxena, is there a need to engage the forum's "heavy artillery'' where a little gun suffices? Your system seems to just begin to lose its ***** charge.
amitsaxena
14-05-2009, 10:07 AM
Dear RIga,
Thanks for your interest as the problem is solved. Its very simple as the drain was chocked.
Thanks
Amit
Yuri B.
14-05-2009, 10:09 AM
Provided filters were clean and the fan operated properly prior to the situation described (and if fan was OK, now, is certainly, blocked with the ice - aggrevating the icing)
icecube51
14-05-2009, 10:48 PM
Dear RIga,
Thanks for your interest as the problem is solved. Its very simple as the drain was chocked.
Thanks
Amit
i think you never going to skip an anual service again.:o
Ice
nike123
15-05-2009, 02:43 PM
Mr. Nike,
Water is continuously dripping from the front grill and Coil is fully frosted.
thanks
amit
If coil is frosted, then problem is not only with chocked drain.:eek:
Probably it is filter clogged and evaporator dirty.
icecube51
15-05-2009, 07:01 PM
so,.....as i said, MAINTENANCE!!!
Ice