In a secondary coolant system we have screw type compressors (HSN 7471-75-40P and CSH 8571-140-40P)and wondering if we need accumulator or not .
On the other word , is liquid return to screw compressors a serious problem ?
Thank u for ur attention.
Regards

NoNickName
27-04-2009, 12:38 PM
That is not the right question.

The question you shall ask to yourself is: "did I make all efforts to avoid liquid floodback?". If not or unsure, install an accumulator.

A_Ahed
27-04-2009, 02:36 PM
We r gonne install but not sure if it is possible to omit it or not ?
Is liquid flood back a threat to screw type compressors or these types can bear in case of a little amount of flood back

NoNickName
27-04-2009, 04:06 PM
Floodback cannot be considered at design time. Not an option.

Then, the compressor may bear it or not, it doesn't matter.

nh3wizard
27-04-2009, 05:06 PM
I would tend to go for the safest approach and install a accumulator.

icecube51
27-04-2009, 07:07 PM
by the way, liquid flood back is hazardus for EVERY type of compressor. the scroll can take and cope better whit flood back,all the others crash and dye.

ice

pirestani
29-04-2009, 04:43 PM
I think it depends on ur cycle and exp.v type, but Im also not sure about necessity of liquid-return protection for screw compressor. if anyone has such exprience I`ll be appriciated to get advises.