in heathing mode after fey minutes starting to flash timer and power laps (middle lamp on 5 way) and door is closing. Please help

boka
28-04-2009, 02:46 PM
Nobody can help?

superswill
28-04-2009, 09:27 PM
can you double check the model reference please,i maybe able to

boka
30-04-2009, 10:01 AM
i check model again is: Samsung power inverter SH12VA1 3.5/3.8kw

superswill
30-04-2009, 04:23 PM
OK the power inverter of that size has not hit the UK yet (to the best of my knowledge) looking at similar models its looking like a indoor pipe thermistor fault or fan motor (give it a spin to check this)

either way looks like you will require a visit from your local service agent

boka
16-05-2009, 02:16 PM
Can someone provide me service manual for this model

boka
21-05-2009, 01:58 PM
I open outdoor unit and on the electronic plate are 3 led diodes red green and yellow. When i run the A/C red one is blinking green is flashing and compreson is trying to run several time and at the end red end green is turned off and everything stops. Maybe this will help to find solution. Thanks