View Full Version : Pump down and suction pressure switches: legacy?



NoNickName
21-04-2009, 09:27 PM
I would like to hear comments on the subject line from field engineers.
As aftersales for compressor manufacturer, I must say that pump down is more harmful than not, because then that procedure is in action the motor is not cooled and no gas is pumped.
The motor overheats, and the rod-shaft assembly is subject to extreme differentials.

Additionally, when the LP pump down switch is unreasonable set to a very low setting, the compressor may be subject to work outside the operational envelope until it finally comes to a stop.

So the question is: how come so many engineers are so fond of pump down procedures? Isn't it time for the industry to realise we are in 21st century and abandon the legacy of old-fashioned habits?

And for you in refrigeration: isn't it time to replace the suction pressure switch with a real thermostat in your cells or freezers. Come on guys: my grandpa used to stop the compressor on suction pressure... there is no place for this in 2009.

Grizzly
21-04-2009, 09:49 PM
I would like to hear comments on the subject line from field engineers.
As aftersales for compressor manufacturer, I must say that pump down is more harmful than not, because then that procedure is in action the motor is not cooled and no gas is pumped.
The motor overheats, and the rod-shaft assembly is subject to extreme differentials.

Additionally, when the LP pump down switch is unreasonable set to a very low setting, the compressor may be subject to work outside the operational envelope until it finally comes to a stop.

So the question is: how come so many engineers are so fond of pump down procedures? Isn't it time for the industry to realise we are in 21st century and abandon the legacy of old-fashioned habits?

And for you in refrigeration: isn't it time to replace the suction pressure switch with a real thermostat in your cells or freezers. Come on guys: my grandpa used to stop the compressor on suction pressure... there is no place for this in 2009.

Sorry nonickname.
I have never doubted your sound and Knowledgeable advise before.
But i have to say there are still plenty of situations where a controlled pump-down is necessary.
How else do you ensure long pipe runs to remote evaporators are void of liquid.
Sure there are plenty of situations where it may be possible to do without the pump-down.
But I can think of many industrial applications where it is necessary.
I am talking about recips here.
Grizzly

NoNickName
22-04-2009, 11:30 AM
How else do you ensure long pipe runs to remote evaporators are void of liquid.


My guess: suction strainers?

nike123
22-04-2009, 05:38 PM
How long pump down lasts? 10-20 sec?
I dont think that that is doing any damage for that short period of time.
Do you have any study to support this:

The motor overheats, and the rod-shaft assembly is subject to extreme differentials.

al
22-04-2009, 09:01 PM
get the pitch forks and set the fire.............

tis a point of view i suppose but like nike is there any evidence??

i do agree that lp cut out can be way too low especially on medium temp stuff, but in fairness all the talks/discussions from comp manufacturers have never pointed out pump down as a main cause of failure or is this a late april fools:)

al

NoNickName
22-04-2009, 10:44 PM
This is not a late april fools. This is a legitimate point of view from a second biggest european compressor manufacturer after sales service, that is me.

And for nike123: yes I have a study. Actually I have more than that: I have an empirical test in the calorimetric lab. And the time of the pump down is limited by the liquid solenoid valve tighteness. It can be well over minutes, if the diaphragm is not refrigerant-tight.

But for what it's worth, whether pump down procedure is letting the compressor out of the working envelope, whether it is 1 second or 1 minute or 1 hour, IT IS FORBIDDEN.

It is true, no manufacturer ever pointed out this as a cause of failure, but there is a first time for everything, don't you think?

Grizzly
22-04-2009, 10:49 PM
Are we at cross purposes here?
A pump down does not have to be in negative pressure so where is the harm?
Grizzly

NoNickName
22-04-2009, 11:02 PM
Are we at cross purposes here?
A pump down does not have to be in negative pressure so where is the harm?
Grizzly

I'm sorry if I'm not clear. Suppose compressor XY has a lower Te at -45°C corresponding to a refrigerant Rxyz at 1 bar(g). This is the lowest left end of the envelope.

Now suppose that at any given time an installing company sets a LP pump down switch at 0.5 bar(g) (remember we are talking about gauges pressure here).

This is clearly prohibited by the same operational envelope, which does now allow compressor to operate AT ANY TIME below 1 bar(g).

This is the POTENTIAL harm.

al
22-04-2009, 11:38 PM
so your solution to no pump down is a suction accumulator(not strainer which does bugger all for liquid!), as a manufacturer are you willing to honour the increased claims due to liquid slugging.........i would doubt it.

Pump down is an economical answer to this problem, again pressure switches should not be set below the recommended settings.

From your own point of view maybe sending the setting information to the wholesalers and a bit of general reeducation would not go amiss??

I do see where you're coming from, though with costs being squeezed i can't see any realistic alternative?

al

modvalve
23-04-2009, 02:05 AM
I would like to hear comments on the subject line from field engineers.
As aftersales for compressor manufacturer, I must say that pump down is more harmful than not, because then that procedure is in action the motor is not cooled and no gas is pumped.
The motor overheats, and the rod-shaft assembly is subject to extreme differentials

You are wrong in saying that no gas is pumped when a system goes into pump down. When a system goes into pumpdown the amps on the compressor drop as the suction pressure decreases as long as it isn't overcharged and the pumpdown never usually lasts more than a minute. I have never seen a motor overheat on a properly maintained system. If you had no pumpdown on a system and it went on defrost you would get severe floodback at the end of the defrost cycle causing more damage to a compressor than pumping it down

US Iceman
23-04-2009, 02:37 AM
Come on guys: my grandpa used to stop the compressor on suction pressure...


And so did mine.:D

I tend to agree with you. If the compressor is allowed to do repeated pump downs on a low-pressure switch you could see motor heating if the liquid line solenoid valve leaks (or some other reason). During this, the motor would have very little mass flow past it for cooling. So... the motor starts and pumps right back down. Repeated start/stop cycles could lead to motor heating as it never really has a chance to cool off. I call this a recycling pump down cycle. This only operates off of a low-pressure switch.

Some will lower the low -pressure switch so that the suction pressure pulls down to a much lower pressure to reduce the short cycling of the recycling pump down. In this case you can be operating outside of the compressor application range and potentially cause increased wear over the same time frame.

On the other hand, if you use a control relay to lockout the compressor until the thermostat calls for cooling and energizes the solenoid valve, the compressor stays off until cooling is again required. I call this a non-recycling pump down, which is what I have used with good success.

Very good discussion going on here....;)

NoNickName
23-04-2009, 08:16 AM
I have never seen a motor overheat on a properly maintained system.

And I have never seen a properly maintained system (or very few in honesty).
And yes, I have also seen a lot of motor overheats, especially by field engineers who start the compressor just after having evacuated the system, and before charging the refrigerant. :rolleyes:
Q: Why are you doing this?
A: I don't have a service valve on the liquid line and don't want to flood the compressor with liquid. So I run it as I start charging. Pooof....


If you had no pumpdown on a system and it went on defrost you would get severe floodback at the end of the defrost cycle causing more damage to a compressor than pumping it down

This is not true. Defrosting, in a properly designed and maintained system, would not cause floodback, if suction accumulator is installed and the coils are fit for purpose.


From your own point of view maybe sending the setting information to the wholesalers and a bit of general reeducation would not go amiss??

That is what I'm going to do, but I wanted to feel the sentiment of the field engineers public on the subject. I'm not going to yell to windmills for nothing.

I tend to agree more with US Iceman, who also introduces some sort of "cultural experience" in the engineering practice, and I appreciate that.

US Iceman
23-04-2009, 02:27 PM
And I have never seen a properly maintained system (or very few in honesty).


This may start a big argument.:eek:

I laughed when I read this and think there is a lot of truth to this statement. Almost any refrigeration system will operate trouble-free for many years if a minor amount of maintenance is performed on a regular basis, if the system is properly engineered and installed.

For any other system not properly engineered and installed your mileage may vary! In this instance the systems last as long as the equipment is able to tolerate the operating conditions or maintenance practices used. Sometimes this is still within the warranty. This is why manufacturers are concerned...

Sandro Baptista
23-04-2009, 04:28 PM
Hi guys,

I agree in some point of with NoNickName but also with Grizzly.

Briefly I would say that:

1) For flooded systems (gravity and pumped) I would never do it because it's not necessary except in some special cases.

2) For medium temperatures I would always made pumpdown (untill the minimum possible allowed by the manufacturer) and if possibly with ventilation connected to ensure that almost all refrigerant has evaporated.

3) In extremely low temperature -40ºC or less I would do it untill the compressor reaches the minimum acceptable. Many many compressors working with this temperatures can go to -45ºC or even less (also depend of the refrigerant). But I also would put a good liquid separador with capability to receive a good quantity of liquid without affect the compressor.

Severals examples I can get to justify the pumpdown (of course if we have a good liquid separator...maybe is not so necessary):

1) When you made an electrical defrost, and if your end defrost termostat is not working well or the probe has a problem it happens that the pressure inside the coil could rise so much (20 bar(a) » 45ºC for R404A) that is bad for the compressor LP limits.

2) It may have condensation of refrigerant in the suction cold pipe far from the evaporator » Result: liquid to the compressor.

3) There is some amount of liquid inside the evaporator coil. The coil can be at temperature of cold store or near after a good while. Then when the compressors starts it will pull gas but maybe it will carry droplets of liquid that are not evaporated untill have a sufficiente temperature difference between the coil and the air of the cold store.

This is my opinion about this subject.

Regards

al
23-04-2009, 06:22 PM
Nonickname

I'm not going to rise to the bait of poorly maintained systems, if this is the case in your country so be it:p


This is not true. Defrosting, in a properly designed and maintained system, would not cause floodback, if suction accumulator is installed and the coils are fit for purpose.


again come back to cost and extra installation time, i'm thinking particularly of smaller systems.

If a compromise were needed then i would definitely be going with icemans suggestion, we do this on most of our serve over installs and also include suction solenoids.

al

US Iceman
23-04-2009, 06:39 PM
One of the things we need to be careful of in this discussion is the issue of context. Different principles and methods are used in industrial refrigeration systems from those that should be commonplace in commercial systems.

Likewise, what should be done in a single compressor/evaporator system may differ from a system where multiple compressors are used in conjunction with many evaporators.

NoNickName
23-04-2009, 08:03 PM
Good points from everybody. Let me further discuss:


I agree in some point of with NoNickName but also with Grizzly.

Ok, flooded, MT and LT. What about HT? I've seen a on-site-built brine chiller for treating sour cream (-5°C approx) with extremely deep pump down. LP switch set to 0.2 bar(g) with R404a. Two 8-cylinders 80HP compressors knocked out to trash, until I decided to steer everybody clear and cut the wires of the pump down switch open. No problem since.


I'm not going to rise to the bait of poorly maintained systems, if this is the case in your country so be it

I'm not going to rise to the bait of chauvinism. Good and bad are widely spread, maybe not homogeneously, but they certainly are.


pressure inside the coil could rise so much that is bad for the compressor LP limits.

And how pump down has anything to do with that? I can't get the point here.


It may have condensation of refrigerant in the suction cold pipe far from the evaporator

Ok, and how pump down will solve the problem? If you have liquid in the suction pipe, pumping down will just lengthen the floodback and liquid ingestion time.
This specific issue is correctly addressed by the simple installation of a suction P syphon and riser with a suction accumulator.


There is some amount of liquid inside the evaporator coil.

Why? Don't you have a liquid solenoid? Isn't your TXV gas tight?


Then when the compressors starts it will pull gas but maybe it will carry droplets of liquid

Have you ever heard of suction superheating? This scenario is impossible, in a "properly maintained system"

al
23-04-2009, 08:29 PM
Good and bad are widely spread, maybe not homogeneously, but they certainly are.


Yes i agree, but your previous statement of never seeing a well maintained system is guaranteed to rise the BP a little!!

The tool that set this should be shot(tool=idiot politely)
I've seen a on-site-built brine chiller for treating sour cream (-5°C approx) with extremely deep pump down. LP switch set to 0.2 bar(g) with R404a. Two 8-cylinders 80HP compressors knocked out to trash, until I decided to steer everybody clear and cut the wires of the pump down switch open. No problem since.


if this had of been shutting off at say 2.5B would there have been a problem, assuming all valves seating
correctly?

al

old gas bottle
23-04-2009, 08:42 PM
my one and only comment, dont lisen to this arrengent asshole, asking for comments then trying to shoot them down with numbers.

pump down works fine.

i,am off on hols for three weeks.

cheers chaps.:D

al
23-04-2009, 08:48 PM
Happy holidays you lucky beggar:p


:off topic:is the girl on the bike going too?? if she's not could i have her phone number?

al

US Iceman
23-04-2009, 09:30 PM
I can understand where this line of questioning came from.

As a manufacturer you are exposed to many warranty issues presented from field service people. A single person or service firm may never see the correlation between one or two compressor failures, however, the compressor manufacturer sees all of them.

From a warranty perspective you try to do the analysis for the failure reasons to see if the defect is due to manufacturing issues or if it is related to field service factors, power supply, or other.

I think what we are seeing here is an attempt to understand how much impact pump down cycles may have on compressors (and the motors). I have seen similar issues with a normal pump down cycle, which is why I used the non-recycling method with the control relay lockout.

old gas bottle
23-04-2009, 10:48 PM
ice man, hello old friend ;) i just dont like the invitation of comments from the "service guys" for ther input ,just to be shot down with a load of technical waffle.:mad:

pump down has been a tried and tested means to an end for a long time now, and as the saying goes "if it aint broke,dont fix it", i,am not big on the keboard but in short, untill the compressor "working enveolope" covers HP/MP/LT,all on the same gas,as well as other relative aspects to do with start pressures after defrost etc , there will be a place for pump down,:)

not saying it wont work without,just majority preferance.:)

US Iceman
24-04-2009, 12:25 AM
HI OGB. I hope you know your avatar is very distracting (very distracting indeed:eek:. In a nice way of course!).

I do not have a problem with pump downs per se, if they are setup properly. That's the reason behind my non-recycling pump down concept. On the other hand, if the system short cycles quite bit then I can foresee some potential problems with motors or contactors/starters.

I understand what you are saying. One of the things with technical discussions is; we need to find some common ground on why the questions are being asked and how the responses are replied to.

As you might guess, manufacturers and service people face different problems. I have been lucky enough (?;)) to have worked in several different fields within this industry and try to have an appreciation for what the other guys are thinking. What I have seen is; we almost always find similar problems or issues, but many different ways to deal with them. Most often though, it is possible to find the root cause and try to find a simple solution using the KISS principle.

Temprite
24-04-2009, 01:36 AM
Dont forget there is this apparent issue regarding pumpdown.:)

www.refrigeration-engineer.com/forums/showthread.php?t=10949

Goober
24-04-2009, 03:15 AM
In response to Temprites thread "to pump down or not to pump down" and to hijack this thread somewhat. I'm in the pump down camp as that's what i was taught right from the start. However, I totally accept and understand Buffola Trident being adamant not to have a pump down on there evaps during defrost. Any mass of refrigerant liquid "under pressure" will most definatley assist in a defrost of any make of coil, I think we're all missing the obvious here in that during defrost the compressor will not run (in non pump down mode) sooooooo.......where is the liquid going to boil off too? Yeah ok some might, but..........Any increase in pressure results in an increase in temperature. (Boyles Law if I'm not mistaken) Ip so facto, or something like that, better defrost is achieved.

Back to compressor issues with pump down. Not an issue as far as I'm concerned. Of course I've had most of my experience in supermarket type work, light commercial, solenoids pumping down all over the place. Comments regarding LP's cutting the compressor off at too low a pressure and leaking solenoids ARE NOT NORMAL. These are fault conditions and of course they will over heat the compressor, etc. In a perfect world everthing would be set correctly, but alas this is not the case. To use this as a reason not to have pump down just does not wash.

US Iceman
24-04-2009, 03:38 AM
Comments regarding LP's cutting the compressor off at too low a pressure and leaking solenoids ARE NOT NORMAL. These are fault conditions and of course they will over heat the compressor, etc. In a perfect world everthing would be set correctly, but alas this is not the case.


And there is the basic premise of the point I was trying to make. By trying to understand the nature of the fault a person can develop a good plan of action for rectifying the issue. Obviously, if the leaking solenoids cause the LP's to short cycle the compressor the answer is to NOT adjust the LP to a lower pressure setting. Find the problem and fix it, not adjust something that reacts to the issue.

This is one of the reason why TXV's get adjusted more than they should be.

Grizzly
24-04-2009, 05:25 AM
NONICKNAME.
May I say I appreciate your dilemma.
When working in the Cold Stores. I and many other Engineers used to despair at the number of idiots (sorry fork truck drivers).
That would hit the chamber doors off or even drive the forks through the doors!
The truth is it's a select few and not everyone should be tarred with the same brush.
Or the ambulance driver that regularly attends fatal accidents.
He is more aware and pays more relevance to it
Than you or I would!
Everyone is refering to motors not cooling.
So I assume an open drive is exempt?
I had never made the connection before.
But i guess that is why most chiller manufacturers have a three alarms and "lock out" Control strategy?
I am beginning to understand what you are telling us.
Based on your experiences, assisted very well by Iceman.
I would just like to add that once informed I try to use that knowledge to better my working practises.
But your original post makes me angry, because as an engineer.
I have never knowingly carried out adverse engineering practises.
Having said that, it is a very good topic.
But I can't see how it is easily resolved?
Grizzly

NoNickName
24-04-2009, 09:21 AM
Thanks everybody for their participation in the subject, even those who reacted instinctively with offense. That's perfectly normal and human, and exactly what happened to tolemaic believers when galileans told them the sun was not revolving around earth.


I think what we are seeing here is an attempt to understand how much impact pump down cycles may have on compressors (and the motors).

Perfect. I think this is much more honest than just write in a small font at the end of the user manual "pump downs not allowed" and put the blame on the installing company.
Chances are that pumpdown harms the compressor, and if prohibited, warranty is void, or no pumpdown is performed, and compressor breaks for liquid floodback which is also not covered by warranty.
Instead than just promoting a stance pro or against, I wanted to feel the wrist of the users. I'm sorry that not being English my mothertongue, I may have been misunderstood.


So I assume an open drive is exempt?

Grizzly, it may be, but not being grand producers of open type compressors, I can't say.


I totally accept and understand Buffola Trident being adamant not to have a pump down on there evaps during defrost.

Goober, what I was taught, instead, is that defrosting is to be made with hot gas when the compressor is running, and by doing so, no liquid goes to the compressor.


pump down has been a tried and tested means to an end for a long time now

old gas bottle, what you are saying here is that your past is what makes you experienced, and I'm fine with that.
Besides I don't accept sentences like "I've being doing that for 20 years now, there must be a reason why" understating experience when in fact you could have possibly mistaking for the last 20 years, without even knowing. Or just a better way you didn't know it existed.
Actually, the most experienced engineers are the ones who are more reluctant in accepting corrections and improvements.

Sandro Baptista
24-04-2009, 09:40 AM
Quote:
<TABLE cellSpacing=0 cellPadding=6 width="100%" border=0><TBODY><TR><TD class=alt2 style="BORDER-RIGHT: 1px inset; BORDER-TOP: 1px inset; BORDER-LEFT: 1px inset; BORDER-BOTTOM: 1px inset">pressure inside the coil could rise so much that is bad for the compressor LP limits. </TD></TR></TBODY></TABLE>
And how pump down has anything to do with that? I can't get the point here.

Before you stop to defrost you evacuate the coil as much you can. Close the EVR and mantain the ventilation running, if possible. If there is a amount of refrigerant inside the coil and due to that if during the the pressure rise above the KP1 regulation then the compressor will pumpdown during.


Quote:
<TABLE cellSpacing=0 cellPadding=6 width="100%" border=0><TBODY><TR><TD class=alt2 style="BORDER-RIGHT: 1px inset; BORDER-TOP: 1px inset; BORDER-LEFT: 1px inset; BORDER-BOTTOM: 1px inset">It may have condensation of refrigerant in the suction cold pipe far from the evaporator </TD></TR></TBODY></TABLE>
Ok, and how pump down will solve the problem? If you have liquid in the suction pipe, pumping down will just lengthen the floodback and liquid ingestion time.
This specific issue is correctly addressed by the simple installation of a suction P syphon and riser with a suction accumulator.

Nonickname, who did said that I would have liquid in the suction pipe? I do the pump down just no to have liquid.

Quote:
<TABLE cellSpacing=0 cellPadding=6 width="100%" border=0><TBODY><TR><TD class=alt2 style="BORDER-RIGHT: 1px inset; BORDER-TOP: 1px inset; BORDER-LEFT: 1px inset; BORDER-BOTTOM: 1px inset">There is some amount of liquid inside the evaporator coil. </TD></TR></TBODY></TABLE>
Why? Don't you have a liquid solenoid? Isn't your TXV gas tight?

Yes I have, but it will remain liquid in the coil and when the compressors starts it will pull gas but maybe it will carry droplets of liquid. Note that after a while the evaporator and compressor stops by cold store temperature achived the mixture of liquid and vapor will be in the two-fase region saturated liquid/saturated vapor »» without superheat.

Quote:
<TABLE cellSpacing=0 cellPadding=6 width="100%" border=0><TBODY><TR><TD class=alt2 style="BORDER-RIGHT: 1px inset; BORDER-TOP: 1px inset; BORDER-LEFT: 1px inset; BORDER-BOTTOM: 1px inset">Then when the compressors starts it will pull gas but maybe it will carry droplets of liquid </TD></TR></TBODY></TABLE>
Have you ever heard of suction superheating? This scenario is impossible, in a "properly maintained system"

Yes I have, but it will remain liquid in the coil and when the compressors starts it will pull gas but maybe it will carry droplets of liquid. Note that after a while the evaporator and compressor stops by cold store temperature achived the mixture of liquid and vapor will be in the two-fase region saturated liquid/saturated vapor »» without superheat.

Nevertheless just I have said before the subject you rise (Pump down and suction pressure switches: legacy?) is logical and correct in some points.

Regards

modvalve
24-04-2009, 10:17 AM
<TABLE cellSpacing=0 cellPadding=6 width="100%" border=0><TBODY><TR><TD class=alt2 style="BORDER-RIGHT: 1px inset; BORDER-TOP: 1px inset; BORDER-LEFT: 1px inset; BORDER-BOTTOM: 1px inset">.




</TD></TR></TBODY></TABLE>
And I have never seen a properly maintained system (or very few in honesty).
And yes, I have also seen a lot of motor overheats, especially by field engineers who start the compressor just after having evacuated the system, and before charging the refrigerant. :rolleyes:
Q: Why are you doing this?
A: I don't have a service valve on the liquid line and don't want to flood the compressor with liquid. So I run it as I start charging. Pooof....

Hi Nonickname
I dont know what kind of standard of work you have in Italy but here in New Zealand we take pride in our work and generaly all systems are well maintained.

As far as overheats by engineers , who start the compressor just after having evacuated the system, and before charging the refrigerant. :rolleyes:
I presume you are talking about little domestic compressors as all commercial /industrial systems would have a liquid line service valve

NoNickName
24-04-2009, 10:28 AM
I presume you are talking about little domestic compressors as all commercial /industrial systems would have a liquid line service valve

No, not the case. You would be surprised how many. And I'm travelling the 5 continents.


here in New Zealand we take pride in our work


Who doesn't?

modvalve
24-04-2009, 11:04 AM
Hi Nonickname

are you going to tell us what compressor manufacturer you work for? over here we mainly see Bitzer and Copeland in the commercial stuff and some NZ manufacturers use Refcomp on their water chillers

nike123
24-04-2009, 12:52 PM
Hi Nonickname

are you going to tell us what compressor manufacturer you work for? over here we mainly see Bitzer and Copeland in the commercial stuff and some NZ manufacturers use Refcomp on their water chillers
http://www.refrigeration-engineer.com/forums/showpost.php?p=117729&postcount=5

US Iceman
24-04-2009, 02:25 PM
So I assume an open drive is exempt?


Not entirely. An open drive motor (especially larger motors) have a limit of hot starts per hour you should heed. This is based on the ability of the motor to naturally cool by radiation, conduction, or natural convection when it is not running. Say a motor has been running for a long time at full load in a hot engine room. The compressor starts to unload and shuts off. When this occurs the motor simply cooks, which affects the life of the winding insulation.

There is a rule-of-thumb that states; for every 10°C rise in motor temperature the motor life is reduced by 50%! Therefore, from a motor perspective the motor would last longer if it was kept running so that the fan could continue to provide cooling of the motor windings.

In a hermetic or semi-hermetic motor there is very little natural cooling when the compressor is off. I suspect these might be more susceptible to shorter motor life for this reason.

sterl
24-04-2009, 05:57 PM
I agree with US Iceman: Pump it down once, properly.

And I believe and on restart, manage the various flows and charges. What is involved does change from system to system, but most of it is control strategy & timing.

Our internal policy is for single-space or one-on-one applications:
-run all condenser fans/flows during pumpdown.
-NO diaphragm solenoids on liquid lines.
-low ambient duty, always manage liquid pressure & holdback from the discharge of compressor.
-Discharge piloted and checked oil return from separator or reservoir.

NoNickName
01-05-2009, 10:34 AM
This may start a big argument.:eek:




http://www.refrigeration-engineer.com/forums/showpost.php?p=143395&postcount=8


Some engineers may agree, though.

US Iceman
01-05-2009, 01:50 PM
http://www.refrigeration-engineer.com/forums/showpost.php?p=143395&postcount=8


Some engineers may agree, though.


I saw this developing into a contest.;)

I have seen the same thing with moisture in the system, improper evacuation, poor commissioning, and overall bad maintenance practice affect the durability and ultimate life of the compressor.

These are simply observations of what I have seen over the last 30-40 years and is not limited to one man businesses! As a manufacturer yourself you see a lot more of this than the person in the local business area since you have to work with the warranty issue.

Peter_1
31-05-2009, 08:15 AM
http://www.refrigeration-engineer.com/forums/showpost.php?p=117729&postcount=5

It was up to NoNickName to respond to this question if he wanted to do this.

nike123
31-05-2009, 08:43 AM
It was up to NoNickName to respond to this question if he wanted to do this.

I thought that if he already made statemant about that in public, that is no harm done by pointing to that.
But, if you thing that pointing affecting his privacy, or is rude, than you have all means to remove it!

NoNickName
31-05-2009, 10:45 AM
I did neither complain nor comment. I simply think it is off topic to mention our companies. Anyone who is interested may just contact me privately off list.

Peter_1
31-05-2009, 02:27 PM
Perhaps the Frascold envelopes are made to narrow or they should state that you can go out of it for a short time to pump down not exceeding some start/stops in 1 hour.

I installed hundreds of compressors and never one failed due to a pump down but several did due to not doing it.

Compressors connected to eutectic plates without suction accumulator and without pumpdown will brake within weeks.
It's the one or the other.

Agree, a suction accumulator can prevent a lot but why installing an additional item which can fail, drip, takes place, makes teh setup more expensive if years of practice has proven so many times that a pumpdown doesn't harm a compressor.

When pumping down, running amp's are seriously reduced, so is the heat formation of the windings also.
I'm almost sure a compressor is much more harmed when running with excessive SH instead of pumping it down 3 to 4 times/hour.

Bitzer even recommends pumping down, so just the opposite.

NoNickName
01-06-2009, 10:01 AM
Peter, pump downs are by their same nature short in time. What I'm worried, and that worries all compressor manufacturer disregarding the colour, is "how long does it take to pump the system down?". It's not an easy question, it all depends on the volume of the evaporator and the tighteness of the LS.
And truck freezers (likd bofrost, eismann's and the like) are built with eutectic plates without the suction accumulator. You know how they start the compressor? Pulsing it until all liquid is digested through the compressor, 30 starts a minute.
Too easy to put the blame on the compressor.


EDIT: opinions expressed in this forum pertain to me and not to my employer.

Sridhar1312
01-06-2009, 11:53 AM
Pump down is essential where you want to shut down systems for seasonal variation and in many cases the oil migrated to evaporator can be recovered by pumping down only.
For all the refrigeration system ist is important especially where you have remote indoor and otdoor unit with lengthy piping

US Iceman
01-06-2009, 01:57 PM
...is "how long does it take to pump the system down?".


And I might add; how long does the compressor operate in a vacuum during pump down? I have seen some systems where the service person set the controls to operate in a vacuum to provide a complete pumpdown.

I'm sure there are some limitations of the dielectric values for winding insulation that could add to the warranty issues for a manufacturer.

From a manufacturers perspective they have no control over how their compressors are applied to system designs. When someone tries a different system design (such as the one mentioned for cold plates) the compressor takes all of the punishment and ends up looking like a warranty issue, when it's not.

old gas bottle
01-06-2009, 07:34 PM
well the problem being raised over this seems to point to far to many LP,S being set inncorrectly or moving after time or whatever, well there are plenty of preset switches on the market now,in some cases they could be fitted as a back up saftey or as a single opperating switch, i,am not againt this at all,maybe a test or overide button would be nice.;)surley not a lot else is needed to eliminate that part of the problem.

i realy cant see the pitfalls of a pump down system,the solinoid shuts down,the loads decreasing,the amps are droping,the condenser is blowing cooler air over a hard worked compressor.[in most cases] all good stuff , soliniod opens, x ammount of pressure hits the LP,away goes the commpressor upto speed before full load is introduced.

i like it and untill i see a better system or equipement that works and lasts doing it i,ll stick as i am. also stopping with round wheels too as they work fine for me.:p

Billy Ray
01-06-2009, 07:59 PM
To be fair to any compressor manufacturer, incorrectly set LP Pump Down switch's do have negative effect on compressor life.

On numerous occasions (example - R404A medium temperature application) we see in the field LP Pump down control switch set to 2 or 3 psi, with a 10 psi differential!!

Why or why i cry. The poor old compressor is sucking a low pressure, which is not necessary. Generally at these low pressure's the oil starts to foam & leaves the compressor.

Additionally, no sooner has the compresor stopped, it restarts because on a low differential setting.

Setting a reasonble cut out point, reasonable differential, an addition of a compressor anti-cycle timer, pump-down is a tried & tested system which works very well.

Billy Ray

Peter_1
01-06-2009, 08:06 PM
...When someone tries a different system design (such as the one mentioned for cold plates) the compressor takes all of the punishment and ends up looking like a warranty issue, when it's not.

USIceman, coldplates are for me just another type of evaporator, I don't see this as a different system design.

With every system you design, you have to know what to look for and how to set safety systems.

For example, coldplates remain very cold for hours, sometimes a whole day and gaseous refrigerant can migrate with a no running compressor to this plates and condens back in a liquid form.

We also used to install an SV switched together with the compressor. So there could not be liquid collecting in the plates: as soon the compressor stopped, the SV closed. But if the system is shutting down for a longer period, you anyhow could have liquid slugging.
So pumping down is a safe way of protecting the compressor.
Or a liquid separator.

If you set your LP below atmospheric pressure, then this is against all normal used rules. If your compressor looses its gas, then you will have the same problems.
It all stands or falls with a good and safe setpoint of the LP cutout and also protected for short cycling.

Like said in a previous post, Bitzer, not a small German compressor manufacturer even recommends it.

US Iceman
01-06-2009, 08:14 PM
Peter, this is what I was thinking of.



You know how they start the compressor? Pulsing it until all liquid is digested through the compressor, 30 starts a minute.


That is a system design problem or very poorly set controls. As a result the compressors absorbs all of the abuse until it breaks.

I agree with you. Cold plates are only a different type of evaporator. Unfortunately some applications are designed with problems in them. When this happens it is almost always the compressor that is impacted. It is for all intents the only rotating piece of equipment within the refrigeration system.

Peter_1
01-06-2009, 08:19 PM
I just edited my previous post a little bit.

US Iceman
01-06-2009, 08:23 PM
I just edited my previous post a little bit.

What you described is how I would do it also.

It is not that the pump down is creating a problem for the compressors. It is how the controls are set or the people working on the system.

NoNickName
02-06-2009, 08:58 AM
Yes, it's not the idea, but how it is abused.
And I think I would still disconnect the pump down switch as soon as I find one.

Peter_1
02-06-2009, 05:43 PM
Then the change is great you will find a lot of compressors broken if you don't first examine the schematic and the logic behind it.
If a control is wrong set, then every system is a dangerous system, like said before , it stands or falls with the proper settings of the controls as with any system.
A system without pump down and a LP set in vacuum is more dangerous than a pumpdown with a correct set LP.

Gary
02-06-2009, 07:33 PM
So the question is: how come so many engineers are so fond of pump down procedures? Isn't it time for the industry to realise we are in 21st century and abandon the legacy of old-fashioned habits?

And for you in refrigeration: isn't it time to replace the suction pressure switch with a real thermostat in your cells or freezers. Come on guys: my grandpa used to stop the compressor on suction pressure... there is no place for this in 2009.

So you are saying that if something has been done in a certain way for a very long period of time, then it must be the wrong way?

Sorry, but that does not compute. Ridicule is not proof, and change is not always a good thing. Winning the lottery is change. A sharp stick in the eye is change.

If you want change, then you need to prove that it is a change for the better. As the person who is advocating the change, the burden of proof is on you.

US Iceman
02-06-2009, 08:02 PM
So you are saying that if something has been done in a certain way for a very long period of time, then it must be the wrong way?


In some respects, doing something for a long time is no indication it has always been done correctly. This is not too much different than offering the response; That's the way we have always done it, so it must be right!

Sometimes you have to read between the lines. I'm not advocating change for the sake of changing something, only if it is done for the proper reasons and based on sound logic.

Gary
02-06-2009, 08:32 PM
In some respects, doing something for a long time is no indication it has always been done correctly.

... or that it has always been done incorrectly. And that is my point. Ridicule is not evidence... one way or the other.

Show us the evidence... and spare us the meaningless ridicule. Such remarks add nothing to the discussion.

Peter_1
02-06-2009, 08:48 PM
Originally Posted by NoNickName
And for you in refrigeration: isn't it time to replace the suction pressure switch with a real thermostat in your cells or freezers. Come on guys: my grandpa used to stop the compressor on suction pressure... there is no place for this in 2009.
This isn't pumpdown for me: a pump down has always a thermostat which cuts off the SV and the LP finally stops the compressor.
What you're describing is regulating the temperature with the LP but this isn't pumpdown for me.

US Iceman
02-06-2009, 09:07 PM
... or that it has always been done incorrectly. And that is my point. Ridicule is not evidence... one way or the other.

Show us the evidence... and spare us the meaningless ridicule. Such remarks add nothing to the discussion.

My purpose in those comments is NOT to ridicule or insight a riot. And I do think they add to the conversation.

What I was trying to get across is that people tend to do the same thing as those that have trained them do (or what they have a seen repeated by others). Some times they may not understand the ramifications of what they do.

Right, wrong, or indifferent, if we think about the basics of what we do and understand the impact of those decisions we can effect a positive outcome.

I believe this intent of the original post is to get some input on the effects of the compressor due to service or installation techniques commonly used. From a manufacturers viewpoint you always want to understand why the warranty failures arise. If you can pinpoint those issues, then you can find a way to minimize them.

That, I think is what NoNickName was trying to find.

Gary
02-06-2009, 09:48 PM
I have spent most of my adult life trying to change the way people trouble shoot systems, without once demeaning them with a comparison to "Ptolemaic believers". Am I taking the wrong approach? Should I be insulting them rather than persuading them?

NoNickName
02-06-2009, 10:56 PM
There are people who only listen when they are insulted at. And I also take that way quite often, in recent times. Sorry for that, but it is exactly for refrigeration engineers, thinking they are right, just because they did it for 20 years time.
One can be right or wrong irrespective of how much time he/she's been doing it.

That's the point behind pump down. It's not good just because our grandpa's did it until retirement and we are pumping down for legacy that makes pump down a good thing.
And it's not even because it's written on a manual from Bitzer!
Look at their manuals: they say they are compliant with low voltage directive 73/23/CEE which was obsolete and replaced by 93/68/EC which in turn is already been replaced by 2006/95/EC!! But please, go ahead, make my day and take Bitzer's word as gospel.

For Peter1: no, that's not pump down. It was a way of showing how obsolete some state-of-industry solutions are. Still controlling refrigeration by suction pressure, instead than measuring the primary physical quantity, temperature.

Gary
02-06-2009, 11:08 PM
Somebody wake me when the actual discussion of the issue begins (yawn).

US Iceman
02-06-2009, 11:21 PM
I think this discussion if nothing else has shown what happens when you challenge conventional wisdom. I am not advocating for one or other here, just the principle.

Now before anyone tries to hang me, think about this; when a question was posed which challenged conventional wisdom what happened? Most of us jumped in with how we do things. Nothing wrong with that.

This is not meant to be self-righteous or condescending on my part, but this was an interesting thread to follow.

Gary
02-06-2009, 11:43 PM
Really? Conventional wisdom was challenged and I missed it? Did I sleep though the part where evidence was presented and logical discussion ensued?

Nope. Looking back through the posts I see a few unfounded assertions and a lot of "I am right and you are wrong and the only reason you don't believe this is that you are stuck in the stone age".

Note that I haven't come down on either side of the issue yet. I am waiting to see the evidence.

US Iceman
03-06-2009, 01:02 AM
What's more important? Trying to understand the nature of the supposition or proposition presented or using sarcasm to respond to posts which might be opinionated?

We all have opinions on something. How we respond to those is another matter.

I'm not necessarily agreeing that pumpdowns and low pressure switches should be avoided, but the underlying problems and how they affect compressor warranties is something I would think we would all interested in.

I would like to see evidence also. But as this is a public forum privately held specifics may not be available.

Gary
03-06-2009, 01:10 AM
I would like to see evidence also. But as this is a public forum privately held specifics may not be available.

I would settle for logical discussion.

US Iceman
03-06-2009, 01:25 AM
OK, let's try a different approach.

Here is the original premise...



... I must say that pump down is more harmful than not, because then that procedure is in action the motor is not cooled and no gas is pumped.
The motor overheats, and the rod-shaft assembly is subject to extreme differentials.


To be fair, we could start with the known facts.

What are the damages to the compressor? - overheated motor & potentially higher operating pressure ratios

The tricky part is trying to correlate those issues to specific failure modes.

So....my question is: How was this determined to be pumpdown related and not high suction/discharge superheat? Either one could have caused similar results for motor burnouts or valve damage.

However, rod-shaft assembly issues would either be lubrication induced or high pressure ratio issues.

Perhaps NoNickName can address these, if we can all be objective.;)

Peter_1
03-06-2009, 07:04 AM
Still controlling refrigeration by suction pressure, instead than measuring the primary physical quantity, temperature.

If you regulate very precise your LP then you're measuring very precise your temperature.
I have some small compressors this way running which were installed around 1970 -1980. The end-users are very satisfied and this long time regulating this way with a satisfied customer is a prove that the installation was set right at the first moment. But if the customer wants it a little bit colder - which isn't needed once regulated- then he need the technician for this.

Peter_1
03-06-2009, 07:10 AM
And truck freezers (likd bofrost, eismann's and the like) are built with eutectic plates without the suction accumulator. You know how they start the compressor? Pulsing it until all liquid is digested through the compressor, 30 starts a minute.

We happen to service some Bofrost trucks (9) because our shop is three shops from me.
They don't have a suction accumulator but they have an SV closing together with the compressor like I mentioned in another post.
But what happens with a normal evaporator when shutting down without an SV? There's also gas migration and liquid can also collect then. So every evaporator can collect some liquid and every compressor can start with some liquid.

Peter_1
03-06-2009, 07:12 AM
I because then that procedure is in action the motor is not cooled and no gas is pumped.
There's still gas pumped, otherwise it should cut out on LP but load is also reduced, so it doesn't need to be cooled that much as in full load.

Peter_1
03-06-2009, 07:17 AM
That's the point behind pump down. It's not good just because our grandpa's did it until retirement and we are pumping down for legacy that makes pump down a good thing.
And it's not even because it's written on a manual from Bitzer!
Look at their manuals: they say they are compliant with low voltage directive 73/23/CEE which was obsolete and replaced by 93/68/EC which in turn is already been replaced by 2006/95/EC!!

It's not because it's not mentioned in their latest manuals they're not compliant with 2006/95/EC.
If I don't hand over a pressure certificate to my client doesn't mean it hasn't been pressurized.
These are just documents - for most techs non saying - and doesn't say anything about the qualities of a compressor.

Peter_1
03-06-2009, 07:24 AM
But please, go ahead, make my day and take Bitzer's word as gospel.

I certainly will do because that the machine we mostly uses because they're for me the Rolls Royce amongst compressors.

And Bitzer affirms what I'm doing already so long.

Reason why so many OEM's uses this machine (packs, icemachines, production machines, oil coolers...)
I suppose if price isn't important but quality is needed.

You have to face it NNN, few agree with your opinion which doesn't say your can not be right.
You're right if controls are set not the correct way but then this is valid for every compressor.

I will anyhow continue pump down my compressors the right way till someone can prove me that what I'm doing can harm my compressor.

Peter_1
03-06-2009, 07:32 AM
The motor overheats, and the rod-shaft assembly is subject to extreme differentials..
Differentials of pressure or temperature?

old gas bottle
03-06-2009, 07:51 AM
i ,am thinking its time for this one to end :eek: i got peeded off when a certain no all starts telling me i,am stuck in the stone age and need to change , that things and people in the industry dont know as much as him even if they have been sucsessfull bussiness men for donkeys years and respected in the trade. most guys on here welcome change if its for the good and i,am in that camp,but insulting someone into change just does not cut it with me:( people skills could have made this a interesting debate instead of a slanging match.;)so carry on,i,am done with this one.

NoNickName
03-06-2009, 07:55 AM
Ok, let's address one issue at a time:



Note that I haven't come down on either side of the issue yet. I am waiting to see the evidence.

The evidence was there for whom wanting to read it since the first post. Operating the compressor out of the envelope is harmful. Full stop. Operating the compressor out of the envelope AND pumping down is as harmful as or even more than.... I think this is crystal clear.


I would like to see evidence also. But as this is a public forum privately held specifics may not be available.

Pump down is not harmful PER SE. Operating the compressor out of the envelope is.


Perhaps NoNickName can address these, if we can all be objective.

Well, I'm not a designer, but it's evident that all machinery operated in conditions not foreseen at design time, may lead to failures, or at least to a shortening of MTBF.


If you regulate very precise your LP then you're measuring very precise your temperature.

No, you aren't. Pressure and temperature are not directly related in a system where more variables are involved and affecting the thermodynamical equilibrium. Eg.: refrigerant charge, pressure drops, etc.


I have some small compressors this way running which were installed around 1970 -1980.

I have too. Is this all about who spits further?


So every evaporator can collect some liquid and every compressor can start with some liquid.

So, it looks like you are following bitzer's manual as soon as it agrees with your pre-concept. Is there anywhere on their literature that the compressor is able to start with "some liquid"?
Truth is that a refrigeration engineer, who shall bear this title, would not let "some liquid" return to the compressor, even when relying on the quality of the compressor itself.
Bad design and bad maintenance, sorry. Warranty unrecognised.


If I don't hand over a pressure certificate to my client doesn't mean it hasn't been pressurized.

It just means you are unlawfully handing over your assembly.
It is irrelevant whether it was pressurised or not. Declaring compliancy to an obsolete directive is like driving in compliance with expired speed limits.


So....my question is: How was this determined to be pumpdown related and not high suction/discharge superheat? Either one could have caused similar results for motor burnouts or valve damage.
However, rod-shaft assembly issues would either be lubrication induced or high pressure ratio issues.

Exactly. The big end of the rod was consumed by excessive differential pressure between crankcase pressure and discharge pressure. It was lubricated, but still it failed after repeated attempts (hundreds or thousands tries) to evacuate the suction. Note: this was a HBP compressor, not a LBP one, therefore the envelope is limited on the left.

Gary
03-06-2009, 04:02 PM
We have all seen pump down systems lasting for many years, so we are not talking about immediate damage, but rather long term damage.

Everything causes long term damage. Simply running the compressor will eventually lead to it's demise.

So the issue then is which strategy leads to the longest/shortest compressor lifespan.

Gary
03-06-2009, 04:27 PM
Demonstrating any of this would require a long term statistical study, preferably under tightly controlled conditions, plotting strategy versus compressor lifespan, and the margin of error would be inversely related to the number of systems involved in the study.

NoNickName
03-06-2009, 04:35 PM
Demonstrating any of this

any of this... what?



So the issue then is which strategy leads to the longest/shortest compressor lifespan.

And what you think in terms of envelope of compressor? Running it outside of the envelope lenghten or shorten its life?

Gary
03-06-2009, 04:39 PM
any of this... what?

If you read the rest of the post you will realize that "any of this" refers to strategy versus compressor lifespan.

Gary
03-06-2009, 04:41 PM
And what you think in terms of envelope of compressor? Running it outside of the envelope lenghten or shorten its life?

What is the envelope based upon?

NoNickName
03-06-2009, 06:33 PM
What is the envelope based upon?

Extensive calorimetric lab testing. For companies adopting ASERCOM scheme, it also encompasses random competitor counter-check.

Gary
03-06-2009, 06:50 PM
Does the envelope describe the conditions for optimum compressor longevity?... or optimum energy usage?... or the optimization of some other criteria? What is the intended usage of the envelope?

US Iceman
03-06-2009, 08:16 PM
The operating envelopes typically specify the extent of the allowable operating conditions the manufacturers have run or considered normal. Part of the purpose of these envelopes is to define the maximum and minimum conditions like maximum and minimum pressure ratios for any given refrigerant/compressor combination.

NoNickName
03-06-2009, 08:22 PM
Does the envelope describe the conditions for optimum compressor longevity?... or optimum energy usage?... or the optimization of some other criteria? What is the intended usage of the envelope?

Sorry to read that you don't know what the envelope of a compressor is for. It doesn't sound quite right for a wannabe refrigeration engineer.
But since you asked... the envelope surrounds the area of combinations of evaporating and condensing pressures for both the compressor current input, discharge temperature and winding temperature to be within specs.
In our case the current shall be lower than MRA (or FLA) and discharge + winding temperature lower than 120°C.
In other words the envelope is to ensure safety and long lasting operation to the compressor.
The testing conditions of superheating and subcooling are determined by EN12900 norm, as well as performance testing conditions.
All parameters are "tightly controlled" in our independently certified lab and run based a precise schedule, after which a metrological verification of tolerances, dimensions and shapes of compressor components are performed on a measuring 3D robot hub (Johansson and Zeiss).

EDIT: during pump down, the compression ratio increases, as HP is governed by condensing control, while suction pressure is governed by the PD switch. As the ratio increases, the discharge temperature increases two fold: lower vapour mass flow rate and increased end-compression temperature.

Gary
03-06-2009, 08:27 PM
I'm thinking it would be fairly safe to say that there are times when every system runs outside the envelope. For example during pulldown... or heavy load... or each time the compressor starts.

NoNickName
03-06-2009, 08:32 PM
I'm thinking it would be fairly safe to say that there are times when every system runs outside the envelope. For example during pulldown... or heavy load... or each time the compressor starts.

Got to the point. Although pulldowns are occasional (and tolerated), pump downs are SYSTEMATIC.
And I can't accept or tolerate a systematic exception. It is no longer an exception, is it?

Gary
03-06-2009, 08:38 PM
You may find this surprising, but I don't much care what you can or cannot accept or tolerate.

US Iceman
03-06-2009, 09:11 PM
Before this degenerates into a discussion of name-calling I suggest we put this on hold for awhile guys. We've had this happen before and it sours everyone's opinion on what could have been a really interesting discussion.:off topic:

Peter_1
03-06-2009, 09:55 PM
No, you aren't. Pressure and temperature are not directly related in a system where more variables are involved and affecting the thermodynamical equilibrium. Eg.: refrigerant charge, pressure drops, etc. .

I perfectly can regulate the temeprature in a coldroom with an accuracy smaller than 1°C with a LP.
I will even say more: this is an exercise students have to make in classroom to better understand the relation between temperature and pressure.

Once a certain system installed with a given length of lines, the pressure drop remains the same as long as system is running. Variation is not that big to see any diffrence.
Refrigerant charge has nothing to do with this when regulating your temperature with the LP cutout.

Refrigerant is fed to the evaporator and there is a precise equilibrium between temperature and pressure.
You once have to follow this in a real life situation and you will see that real life is different than you have in your mind now.
The LP then even acts as adefrost control.

Peter_1
03-06-2009, 10:05 PM
So, it looks like you are following bitzer's manual as soon as it agrees with your pre-concept. Is there anywhere on their literature that the compressor is able to start with "some liquid"?
Truth is that a refrigeration engineer, who shall bear this title, would not let "some liquid" return to the compressor, even when relying on the quality of the compressor itself.
Bad design and bad maintenance, sorry. Warranty unrecognised.

.
I already quoted also the Copeland manuals.
I'm not following Bitzer nor Copeland's manual. It's only showing you a written evidence that other manufacturers claims just the opposite what you're trying to say. They deliberately write it in their manuals for some reason.
They recommend it.

I do it because I'm convinced of the usefulness of this.

No compressor may start with liquid but if you don't pump them down like you propose, then they often will start with some liquid.
So what's then the best or the worst for a compressor: no pumpdown and start with some liquid or pumpdown and having no liquid?

It's not a pre-concept of me, it's a since long proven good practice used by almost everyone.

Peter_1
03-06-2009, 10:18 PM
All parameters are "tightly controlled" in our independently certified lab and run based a precise schedule, after which a metrological verification of tolerances, dimensions and shapes of compressor components are performed on a measuring 3D robot hub (Johansson and Zeiss).

EDIT: during pump down, the compression ratio increases, as HP is governed by condensing control, while suction pressure is governed by the PD switch. As the ratio increases, the discharge temperature increases two fold: lower vapour mass flow rate and increased end-compression temperature.


With a 3D robot, you're measuring distances. How then you mesure differences on a compressor which ran with and one without pumpdown?
And after how many cycles do you measure then?
I'm sure this was never examined in your lab extensively.

This could have been a firm prove of your theory which remains only a certain theory, a personal vision.

NNN, while pumping down, your HP decreases a lot - era when HP was maintained on a stable HP is long time ago - because load decreases while pumping down.

AMP's are also going down very fast while pumping down.

And what do you do then when it's becoming hot outside and HP increase and DP then also increases?
DP then increases the same as when you pump down.

NoNickName
03-06-2009, 10:43 PM
I perfectly can regulate the temeprature in a coldroom with an accuracy smaller than 1°C with a LP.

You can't be serious.



I will even say more: this is an exercise students have to make in classroom to better understand the relation between temperature and pressure.

My students would be rejected as any of them will try to control a cold room temperature with a LP switch.



Refrigerant charge has nothing to do with this when regulating your temperature with the LP cutout.

Refrigerant charge affects subcooling. Subcooling affects cooling capacity. Cooling capacity affects evaporating pressure. Enough said.



Refrigerant is fed to the evaporator and there is a precise equilibrium between temperature and pressure.

There is no precise equilibrium between suction pressure and cold room temperature.
Sorry. As I said, charge affects it, as well as coil clogging, frosting, air circulation... and anyone trying to set a precise temperature in a room with a pressure switch he'd be better turn back to the drawing board.


The LP then even acts as adefrost control.

Oh, yes, I've seen a lot of system defrosting a feather-clogged but otherwise frost-free coil.


With a 3D robot, you're measuring distances. How then you mesure differences on a compressor which ran with and one without pumpdown?

That is not the point. The measurement is for analysing the expected life time and repeatability of tests carried on inside of the envelope.


I'm not following Bitzer nor Copeland's manual. It's only showing you a written evidence that other manufacturers claims just the opposite what you're trying to say. They deliberately write it in their manuals for some reason.
They recommend it.

None of them recommends to start their compressors with "some liquid". Please stay on topic. And please, I am a man, not a manufacturer.


era when HP was maintained on a stable HP is long time ago

About the same age when pump down was introduced or was it later...

Again, compressor manufacturer recommendation must be complied with, disregarding color and brand. When compressor is operated outside of the limits, the compressor may be affected and eventually break. If the compressor is pumped down repeatedly at a lower-than-allowed pressure, it is a direct responsible of a possible developing fault.
I think the above is agreeable in principle by anyone, advocating pump down or not.

al
03-06-2009, 11:04 PM
NNN

Would it be true to say that so long as the compressor remains within its "envelope" you have no problem with pump down per se?

al

Gary
03-06-2009, 11:27 PM
Again, compressor manufacturer recommendation must be complied with, disregarding color and brand. When compressor is operated outside of the limits, the compressor may be affected and eventually break. If the compressor is pumped down repeatedly at a lower-than-allowed pressure, it is a direct responsible of a possible developing fault.
I think the above is agreeable in principle by anyone, advocating pump down or not.

If this is true, then you could simply refuse to honor warranties for pump down systems. Then the only remaining question would be how deeply your more tolerant competitors bite into your market share.

I'm thinking it would be more in your interests to persuade rather than dictate.

NoNickName
04-06-2009, 07:29 AM
NNN
Would it be true to say that so long as the compressor remains within its "envelope" you have no problem with pump down per se?



Sure, and for that the refrigeration engineer shall have the appropriate compressor envelope with him when setting and commissioning the PD switch.

And for Gary, if pump down is within compressor envelope, no reason not to honor warranty.

At this time, no action is taken on these regards (dictation or persuasion) and in terms of tolerance the company I'm hired to is known to be the most tolerant to clients abuses.

Peter_1
04-06-2009, 07:38 AM
nnn, as usual, if others don't follow your truth, your thinking, you start to play it very personally or you pointing posters back as a teacher if they're leaving the thread.

Difference between us, i did it all with my own hands since more then 25 years. I gained my experience not only behind my desk.

I'm not someone who solely relies on what 's found behind a desk and a lab.

And after all those years, I found the time right to share what I've learned over all those years with others. That's when I started school Allessandro, not sooner.

NNN, I'm very serious saying I can control a cold room within 1°C with the LP.
Fact you doubt this is for me a sign you better leave a little bit more your desk and lab to gain some real world practice and real-life experience in a much broader field then only 1 brand of compressors and one brand of heatpumps.

And I don't believe everything what others saying and what I find in books or manuals.

NoNickName
04-06-2009, 07:49 AM
I come from the field and have 15 years experience hands-on. I am behind the desk since only one year. Therefore, I don't accept being taught.

If you are sharing with others the knowledge that temperature shall be controlled with a pressure switch, then I understand why this refrigeration world is going down the flush.

FreezerGeezer
04-06-2009, 01:02 PM
OK gents, I think the MAIN problem here is that a lot of you are talking in a foreign language here & not understanding each other properly. As a brit myself I'm finding much of this thread difficult to follow, trying to interpret your versions of my language. I mean no offence, I haven't enough of any other language to even begin to discuss this subject in yours & applaud you all for being able to do so in mine.
Please let's all cool off a bit eh? :)

Sandro Baptista
04-06-2009, 01:50 PM
Guys let's see if all of you (NoNickName and the others agains't the NNN ideas) agree with this and all come back to be friends :D

Briefly I would say that (and it's what I consider for the good operating of the refrigeration plants):

1) For flooded systems (gravity and pumped) I would never do it because it's not necessary except in some special cases.

2) For medium temperatures I would always made pumpdown (untill the minimum possible allowed by the manufacturer) and if possibly with ventilation connected to ensure that almost all refrigerant has evaporated.

3) In extremely low temperature -40ºC or less I would do it untill the compressor reaches the minimum acceptable. Many many compressors working with this temperatures can go to -45ºC or even less (also depend of the refrigerant). But I also would put a good liquid separador with capability to receive a good quantity of liquid without affect the compressor.

Case close??:D:D

Gary
04-06-2009, 04:16 PM
OK gents, I think the MAIN problem here is that a lot of you are talking in a foreign language here & not understanding each other properly.


This is entirely possible. For example, perhaps when NNN says "shall" he really means "should" which would change the tone of his comments from demanding to persuading.

On the other hand I'm thinking that his insults are intentional and strategic.

Gary
04-06-2009, 04:27 PM
Getting back to the issue at hand:

If we accept that the envelope describes the ideal conditions, then we can say that operation outside of the envelope (however brief), while not necessarily "wrong" is "less than ideal" and should be minimized.

Gary
04-06-2009, 05:39 PM
I have zero experience in system design, albeit a pretty fair understanding of how things work. With this in mind, here is how I would design a pumpdown system:

I would install a vertical suction/liquid heat exchanger (HX) alongside the end of the coil, with the suction entering the bottom and exiting the top.

I would mount the TXV bulb on the suction line at the exit (top) of the HX.

On shutdown the liquid line solenoid (LLS) would close. A low pressure control would then shut down and lock out the compressor at a low point which is within the operating envelope of the compressor.

During the off cycle, liquid would accumulate in the coil and/or the HX.

On startup, the compressor would run but the LLS would remain closed.

When the low pressure again reaches a low point within the envelope, the LLS would open.

Gary
04-06-2009, 07:24 PM
Being a radical departure from standard design practices, I would expect that the HX with TXV sensing bulb at it's outlet would be the least understood part of my design, so perhaps I should elaborate:

During the run cycle, this maximizes subcooling/minimizes flashing thus increasing the efficiency of the coil.

Placing the TXV sensing bulb at the HX oulet ensures that the superheat reaching the compressor inlet is the same as if the HX were not there (while maximizing subcooling).

During the off cycle, The HX forms a U shape with the coil, trapping any liquid in the coil and HX.

During defrost the HX, being within the refrigerated space, becomes the coldest part of the system; the part to which the liquid must migrate.

Gary
04-06-2009, 07:29 PM
The other non-standard part of this design is the delay of the LLS.

Just as charging vapor into a system from a container does not allow liquid transfer, delaying the opening of the LLS ensures that the liquid can be drained from the coil and HX only in vapor form.

NoNickName
04-06-2009, 07:31 PM
Please feel free to rephrase my posts to reflect the politically correct and acceptable version of the technical discussion, as long as the main message is untouched.
I don't feel guilty for hurting the sensibility of the audience.

For Gary, although I appreciate your efforts in explaining how you would design a pd system, actual experience says the state-of-the-art is else way. It could be a new chapter for a troubleshooting handbook.

Gary
04-06-2009, 07:39 PM
Please feel free to rephrase my posts to reflect the politically correct and acceptable version of the technical discussion, as long as the main message is untouched.
I don't feel guilty for hurting the sensibility of the audience.

For Gary, although I appreciate your efforts in explaining how you would design a pd system, actual experience says the state-of-the-art is else way. It could be a new chapter for a troubleshooting handbook.

I should add that if you don't agree with my radically new design then you must be stuck in the stone age. :p

Blueboy
04-06-2009, 07:44 PM
May I suggest that properly designed compressors have run for many years trouble free and have pumped down hundreds and hundreds of times. It sounds to me like we are talking about a sub-standard product here. I have worked of systems big and small and have seen the damage that can occur when a solenoid valve fails and a compressor is smashed up by liquid. There are horses for courses and in many situations today a correctly set up pump down system is a simple and cost effective way of ensuring that the compressor is protected from liquid and high starting torque.

By a good quality product maintain it well it will last a long time.You get what you pay for

Gary
04-06-2009, 08:24 PM
May I suggest that properly designed compressors have run for many years trouble free and have pumped down hundreds and hundreds of times.

My experience is the same. That's why I say that the very worst that can be said of pumpdown systems is that they may (or may not) be less than ideal, depending upon your level of faith in the manufacturers operating envelope.

They are certainly not a bad strategy, nor even a sub-standard strategy. But less than ideal? Maybe.

NoNickName
04-06-2009, 09:02 PM
I should add that if you don't agree with my radically new design then you must be stuck in the stone age. :p

Oh, no, I support you.

Blueboy: we were talking about a concept, not about a product. It just started as a personal experience, but I wanted to enlarge it to meta-level.
There are engineers and sub-standard engineers, nonetheless what we are discussing on this forum is best-effort pratice.

US Iceman
04-06-2009, 11:49 PM
If we accept that the envelope describes the ideal conditions, then we can say that operation outside of the envelope (however brief), while not necessarily "wrong" is "less than ideal" and should be minimized.

I would agree with that.

:off topic:
In fact, I have been guilty of operating compressors outside their envelopes at very low condensing pressures. Manufacturer did not recommend it, but it worked just fine.

The envelopes are the generally recognized allowable limits. For instance; Copeland does not catalog compressors for cascade systems, but they still sell them! The end result is though, someone is taking responsibility for it.

I did on those compressor above. It's important to understand what the limits are and try to stay within that envelope unless you are willing to buy new compressors!;)