View Full Version : Fan cycling control



NEW GUY
16-04-2009, 03:38 AM
when using a fan cycling control on a outdoor condensing unit how do you determine what the cut out and cut in should be.

thanks guys:D

NEW GUY
16-04-2009, 03:41 AM
when using a fan cycling control on a outdoor condensing unit how do you determine what the cut out and cut in should be.

thanks guys:D


was gonna ask somethibg else but had a brain fart

ateeq.baig
13-05-2009, 10:47 AM
cut out and cut in depends upon your refrigerant you should mention the type of refrigerant after that any one will be able to send you the actual cut in and cut out

D.D.KORANNE
13-05-2009, 12:21 PM
Steps involved :
a) Check the acceptable / lower condensing pressure from the TEX valve when used
b ) find out the lower condensing pressure wherby the TEX valve does not contribute to hunting
c) if the design & lowest condensing pressure gap is too wide , decide the number of steps & set your cycling pressure controller or teperature signal accordingly