I've been sent down south to reinstate a cooling tower due to on site Engineer struggling to get flow over the tower. After filling the pond and checking strainers and bypassing tower bypass valve I reinstated the chillers. After finding crancase htrs down, leak on oil sight glass,1 chiller tripped on freeze protection due to sequence stat having no probe,trend system allowing tower fans to enable over 50 degree this tripping on head pressure I now know the term engineer is a broad term for some of the ****e engineers that are out there!!!!!

Brian_UK
14-04-2009, 11:18 PM
"Welcome to the real world" is I believe the correct terminology.

Gain some satisfaction from the knowledge that you have got it going and the customer is a little happier.

Don't expect too much from your governor though, he'll want to know why it took you so long to fix it ;)

install monkey
15-04-2009, 08:47 PM
Now gotta fix the pipework on the dosing equipment cox it froze up, now scrimping parts off 1 chiller to get all the others going until the owner goes for city multis