View Full Version : Modulating valve
I am in search of a 2way modulating valve for chilled glycol coils. Not finding many choices. does anyone know of manufacturers ?
Brian_UK
13-04-2009, 10:51 PM
Well here's the first one I Googled...
http://dticorp.com/catalog/honeywell-vc7934zz31-modulating-actuator-series-valves-p-2239.html
Second...
http://gothermal.thomasnet.com/advanced/valves-3/vb2-series-two-way-actuated-ball-valves?&forward=1
Thanks for the reply. I am looking for something more substantial. I am working with coils in the 10 to 25 ton range and I am looking for valve sizes of 1 1/2" on up.
Brian_UK
13-04-2009, 11:44 PM
OK, understood, I'll see what we can find.
TRASH101
14-04-2009, 10:06 AM
You could try electrocontrols
http://www.electrocontrols.co.uk/datasheets/V04.pdf
good luck
jcoffey
21-04-2009, 11:25 PM
Honeywell V5011 series valves with a ML7421 series actuator will give you 0-10 VDC, 2-10 VDC or 4-20 ma control. A simple, yet highly accurate controller would be a Honeywell T775 controller.