Hi member!

I have one system: outdoor(Rx10my1-cooling only) and 4 indoor.
- test and commission : ok
- run mode cool :ok
But i can't find the master of indoor unit in remote.
I know heatpump have the master of indoor
Have master in cooling only?

nike123
10-04-2009, 07:42 AM
Hi member!

I have one system: outdoor(Rx10my1-cooling only) and 4 indoor.
- test and commission : ok
- run mode cool :ok
But i can't find the master of indoor unit in remote.
I know heatpump have the master of indoor
Have master in cooling only?

You don't have need for "master" in cool only, since there is no cool/heat mode switching, and therefore, no possibility of conflicting commands.

thuydsc
10-04-2009, 11:18 AM
Thanks for reply!
But I have a question:
- heatpupm (3mode): heat , cool, fan.
- cooling(2 mode): cool, fan.
When i want to run the system in the fan mode that i chance it by master of indoor.

cool#9
10-04-2009, 06:41 PM
Thanks for reply!
But I have a question:
- heatpupm (3mode): heat , cool, fan.
- cooling(2 mode): cool, fan.
When i want to run the system in the fan mode that i chance it by master of indoor.
Hello
There's no problem to change from cool, dry or fan mode but if you really want to set a master indoor do the code 22 / 9.01 to 9.02 this could be helpfull for other dear RE member....
rgds
cool#9

thuydsc
13-04-2009, 04:15 AM
Thanks alot!

thuydsc
11-06-2009, 10:41 AM
Hi !
Today i come back this building.
I set code 22 / 9.01 to 9.02.
After confirm, remote controler display 88.
Then i set mode fan in this remoter but other remote no chance fan.

CooL#9: is this correct?

El Padre
11-06-2009, 01:39 PM
Hi,
If you power the system down and then back up again the first controller to have the mode button pressed becomes the master.

Cheers

thuydsc
12-06-2009, 04:03 AM
Really !

Thanks alot

Obi Wan
14-06-2009, 11:45 PM
Hi member!

I have one system: outdoor(Rx10my1-cooling only) and 4 indoor.
- test and commission : ok
- run mode cool :ok
But i can't find the master of indoor unit in remote.
I know heatpump have the master of indoor
Have master in cooling only?




thuydsc,

On cooling only VRV systems you can’t select a cool heat master. The outdoor unit is in cooling mode at all times. You can select each indoor unit between cool, fan and dry modes but this is only by the remote controller.

You could try to link the terminals C and B on the outdoor terminals which may switch the entire system to fan only. I have not tried this on a cooling only myself, but it might work.