PDA

View Full Version : Charging Problem



ISOSEEL
03-04-2009, 09:45 PM
Hi Guys, I'm a newly qualified engineer and I am having difficulty charging a monoblock coldroom unit, as I can only find 1 service valve, which is connected to a pipe which comes out only 8-10cm from the compressor.

Do I still charge through this valve as liquid as per normal?

Thanks

nike123
03-04-2009, 10:25 PM
Use gauge manifold valves to meter liquid from refrigerant bottle and it should be OK. Charge in 5% of total weight steps and allow some time in between steps that liquid evaporate. Don't rush!

Graham
13-04-2009, 11:32 AM
I've heard of using a length of copper tubing 1/4" about 3 or 4 meters long, coiled in a bucket of hot water, charge slowly via this tube and avoid the dangers of charging with liquid.

richardb14
13-04-2009, 08:44 PM
have you changed the compressor? why are you recharging it.

what refrigerant is in it?