PDA

View Full Version : carrier chiller hp problems



pobbo
02-04-2009, 04:29 AM
G'day
i have a carrier Chiller 30GB-210.940
Unique No. 30GB.210 OOO571
S/N 0697W09089
Unit has had a History of tripping HP on 30+(c) days
Pipework does not seem to distribute hot gas evenly and bottom horizontal coils do no work
anyone else had a similar problem chiller is about 12 years old

Tesla
02-04-2009, 06:50 AM
Hi pobbo
Check the HP sensor callibration and superheat and subcooling - aim for about 10k subcooling. Also check comp current, ref charge, and obviosly condition of heat exchanger. If the heat exchanger is degraded reduce ref charge. Look for any modification on liquid line ie smaller drier fitted. Check the above with a good load.

Grizzly
02-04-2009, 09:38 PM
pobbo.
Welcome, I cannot really add much to Tesla's excellent advice.
Other than to ask what you mean by the following- "bottom horizontal coils do no work"

Is it because the fin condition has deteriorated so that there is poor flow through them?
Or they may be oil logged?
Damaged?
System overcharged?
Put me out of my misery, what is wrong with them.

If it is down to old age etc. I have resorted to the old lawn sprinkler trick!
Mind we don't suffer from water shortages as much over here.