How to convert refrigerant load to elect load.

Say eg: from 2,400,000btu/hr to kw.



Thanks & Regards

desA
23-03-2009, 02:05 AM
Have you read up on the term:

COP = coefficient of performance ?

sparo
23-03-2009, 05:55 AM
no have not read that.
just want to find out the power consumsion.

icecube51
23-03-2009, 08:22 PM
Sparo, your laizy, google on to Wikipedia and type C.O.P ,coifficient of performance, and you get all the info you want.

laizy bom, Ice

multisync
23-03-2009, 09:21 PM
2.4m BTU -that's a fair old tonnage!

(Just to confuse things further ;-)

atifaslam
18-05-2009, 07:15 PM
Hi All,

How to convert refrigerant load to elect load.

Say eg: from 2,400,000btu/hr to kw.



Thanks & Regards
To convert 2400000 btu/hr to kw procedure is

1 btu/hr is equal to 2.928 kw so u convert easily .ok buddy.

Brian_UK
18-05-2009, 07:21 PM
^ but that is not the electrical consumption required which was his question.

HallsEngineer
19-05-2009, 02:12 AM
Just commissioning 2 chillers in Minnesota at 5.5M BTU/hr each. had to convert everything to kW ref load to BTU and C to F time the americans joined the rest of the world and used SI i say.

D.D.KORANNE
19-05-2009, 01:01 PM
240,0000 btu/hr = 200 TR

2OO TR DIVIDED BY 0.2845 = 702.98 KW

nike123
19-05-2009, 01:54 PM
Hi All,

How to convert refrigerant load to elect load.

Say eg: from 2,400,000btu/hr to kw.



Thanks & Regards


240,0000 btu/hr = 200 TR

2OO TR DIVIDED BY 0.2845 = 702.98 KW


^ but that is not the electrical consumption required which was his question.

:eek:.........................................

Yuri B.
19-05-2009, 08:21 PM
I use such, however, a very, very rough conversion: 1000 W electrical = 3000 W heat = 9000 Btu (also "heat", of course), simply, a mnemonic: 1-3-9, and vice versa.

Yuri B.
19-05-2009, 08:30 PM
This concerning the choice of a comp for an AC. I believe, I have not confused the numbers unforgivably.