View Full Version : Freezer Flatlining



SULTAN
20-03-2009, 11:44 PM
I got a ColdTech/Minus Forty upright single door freezer which is giving me some problem.

What i mean by flatlining is that it never reaches its designed temperature which is set by thermostat.

Set point is set for -20 F But it only reaches to about -9 and keeps cycling.

Its charged with 404
Temperature probe is properly installed
Control was replaced with new digital one but no luck.

What could it possibly be?

tony--1
21-03-2009, 03:36 AM
is r404 on the cascade side of it. just thats a bit cold for r404. need mo info ie. is there a subcooler ? wat is the second stage doing ? (if it has 1 )pressures stuff like that

SULTAN
21-03-2009, 11:57 AM
This is not a cascade system.. Its a upright single glass door merchandiser.
Its a closed system.

Slatts
21-03-2009, 12:17 PM
You say:
Set point is set for -20 F But it only reaches to about -9 and keeps cycling.
So what is it cycling on?
if not the thermostat, is it cycling on an LP control?

SULTAN
21-03-2009, 01:21 PM
This unit has a digital controller that can be adjusted. I changed the controller and still same thing.

I finally solved the mystery and it was low refrigerant that was causing it to have low SC and High SH

tony--1
21-03-2009, 05:03 PM
sultan

not much of a mystery after all . if it was just short of gas .

Slatts
22-03-2009, 12:19 AM
So where was the leak?
I trust you found and fixed it?