hie guys ,i have got a problem with a multistack chilled water plant supplying three floors.when i switch it to manual , pumps are running ,but the chiller is desplaying a message"CHILLED WATER INTERLOC OPEN" , so i cant not understand this ,can someone help?

Brian_UK
16-03-2009, 03:02 PM
Is there a water flow problem?

Is the water flow switch contact closed?

adam0606
30-10-2010, 09:26 PM
The Flow switch on the water pump open. Chiller won't run until switch closes...

Brian_UK
30-10-2010, 10:43 PM
Think we told him that seven months ago. :D