PDA

View Full Version : inside split a/c systems



slothslag
05-05-2004, 01:23 AM
can someone tell me where i can find information of exactly what is inside and split a/c unit (mainly the outdoor unit) in terms of refrigeration components; pipes, valves etc. (not really electrical components).

im particularly interested in daikin. do they have a technical website or something?

thanks,

paul :)

Jasper
05-05-2004, 06:24 AM
COMPRESSOR
CONDENSER
EXPANSION DEVICE
ACCUMULATOR (possibly)
ELECTRONIC CONTROL BOARD


All A/C condensing units contain these components, Heat pumps Also have a reversing valve, :)

slothslag
05-05-2004, 07:43 AM
would my daikin split use a capillary tube or txv? where would it be? inside the indoor unit or the outdoor unit??


cheers

Paul

Latte
05-05-2004, 09:21 AM
Try www.daikin.org.uk/internet/uk/home.nsf

Should be plenty of info on here

Regards

Raymond

chemi-cool
05-05-2004, 02:01 PM
hi paul,

it would also cotain, leaves from the closest tree, dead lizards, pieces of stikcs that kids push into the fan. :D

the expention device - cap tube will be betwen the bottom of the condenser and the liquid line valve.

cap tube used to be in the indoor unit but it makes high noise when when the refrigerant starts flowing or when there is refrigarnt shortage.

from that reason, it was moved into the outdoor unit.

chemi

frank
05-05-2004, 08:09 PM
What - No FAN jasper??? :D

slothslag
06-05-2004, 02:28 AM
thanks chemi :-)

Jasper
06-05-2004, 04:37 AM
I think he said NOT ELECTRICS franf :D :D

frank
06-05-2004, 07:48 PM
ELECTRONIC CONTROL BOARD

So this is not electrical then Jasper? :D

chemi-cool
06-05-2004, 07:54 PM
just shoot him frank :D

chemi :)

frank
06-05-2004, 08:00 PM
Paul

Try this link - it's to a page on the Spaceair members site and it shows the technical liturature (sp?) for a Skyair system. If you scroll down you will find the schematic for the outdoor unit. Hope the link works as I'm a member but I can't give out my password - if I did I'd have to SHOOT you (as Chemi say's) :D http://www.spaceair.co.uk/cgi-bin/pages/skyair/RYP/RYP-L-B%20121%20tech.pdf

Be patient it takes a while to load and is in pdf format

Jasper
07-05-2004, 06:12 AM
DOH :) :D :eek:

slothslag
07-05-2004, 08:18 AM
thanks frank,

thats the kind of diagram i am looking for. only for a mini split though. i guess its prob about the same

one question below....



cheers paul

rbartlett
07-05-2004, 06:05 PM
distributor -as a guess

cheers

richard

chemi-cool
07-05-2004, 06:27 PM
hi slothslag,

indeed its a distributor!!

chemi

frank
07-05-2004, 08:05 PM
10 out of ten boys - it is a distributor. :p

Paul - this is the small device on the end of the liquid line where it splits in to many small pipes to distribute the refrigerant equally into the evaporator. Give me the model number of the split and I'll see if I can post a link for you.

Peter_1
08-05-2004, 06:44 AM
Fire Sprinkler mounted upside down?
Distributor? Only one injection soldered of the distributor?
Rest is open? Wouldn't the gas not blow out the others?
:p :D

Bones
08-05-2004, 01:55 PM
symbol for venturi, indicates a multifed coil is used.

Bones
08-05-2004, 01:58 PM
aka, distributor...

however upon further inspection i too along with peter am abit worried about where the gas is going... ;)

slothslag
10-05-2004, 05:26 AM
Hi Frank,

on the outdoor unit it says its a Daikin RXD71JVEA

remember I live in australia so i dont know if that means different model numbers,

if you could direct me th where i could get a piping diagram; that would be great

:-)

cheers paul

rick
31-10-2004, 12:24 PM
Paul unit is a 3hp r22 inverter,reverse cycle.
Layout of system as follows (On cooling from suction line).
Stop valve.
Reversing valve.
Accumulator.
Compressor.
Muffler.
Reversing valve.
Header.
Outdoor coil.
4 small capillary tubes in parallel
Distributor.
Muffler.
Motor operated valve.
FIlter.
Stop valve.

Regards.