View Full Version : Clivet chiller
philjd26
02-03-2009, 12:53 PM
hi,
i am finding it very difficult to get any useful info on clivet chillers..has anybody got the fault codes at least? i am getting E01 and E31, the model in WRAT-242.....
rgrds phil
narkom
02-03-2009, 08:01 PM
Hi!
What is the controller model?
quiksilva
22-03-2009, 09:32 AM
Phil
just seen this, if we are talking about the model with a red led readouts (3 digit and 2 digit) then E01 is hp trip circuit 1, e31 not shown in my book but an E21 is hp trip circuit 2 and e41 flow alarm on water side hope this helps
andy
1torr
22-03-2009, 02:47 PM
These codes corespond to a CVM 2 controller on a WRAT Climavenita chiller. Sure its not a Climavenita chiller? Cheers Kev.
Grizzly
22-03-2009, 03:20 PM
These codes correspond to a CVM 2 controller on a WRAT Climavenita chiller. Sure its not a Climavenita chiller? Cheers Kev.
Hi Kev.
The codes appear to be the same.
Obviously both companies have not strayed from the carel originals?
I have questioned this myself previously.
Steve.
narkom
23-03-2009, 06:10 AM
Nice Clivet site
Clivet (http://portal.clivet.it/Navigator/navigator.jsp?v_lingua=2)
nike123
23-03-2009, 07:32 AM
Nice Clivet site
Clivet (http://portal.clivet.it/Navigator/navigator.jsp?v_lingua=2)
Thank you Narkom! Just what i need.;)
Grizzly
24-03-2009, 05:53 AM
:DGood Link
Thanks Narkom
Grizzly
E01-Evaporator antifreeze alarm-check the water flow and the probe resistance bydisconnecting it to its terminals.
E31-Module 1 off network- check the serial addresing card.
Powered by vBulletin® Version 4.2.1 Copyright © 2024 vBulletin Solutions, Inc. All rights reserved.