hi everyone,im just getting started out on RE but would like to ask does anyone know if it is possible to change the mitsubishi g50 controllers min cooling set point to >19degrees have a costomer who has just decided he wants it at 17 for no reason :rolleyes: got onto mutsi but no joy any body come across this before????

HeathT
24-02-2009, 09:55 PM
The G50 in cooling mode has a setpoint range of 19-30 celsius so unfortunately for your customer 17 is not achieveable. Any reason for such a low setpoint?

dcool
24-02-2009, 10:46 PM
ya im running the g50 on a heat pump system with 3 condensers and 3 ducted units in controlled enviroment [lab] i think its because a previous job we did was with daikins so to the set points can go to 16 was thinking about off setting the return air probe with a 1ohm rest what do you think???

superswill
24-02-2009, 11:06 PM
is it sized to pull down to 17?

dcool
24-02-2009, 11:33 PM
hi paul ya mate its well able to do the job have 3 25 kw units on with a 60kw load on or test runs over 2 hours the room temp dropped to 13 degrees so that wont be a problem im just thinking if i off set the termsistor will it cause me problems down the line this guy wont give up on this one :eek:

nike123
25-02-2009, 08:03 AM
You could offset by 2K ambient air thermistor by adding resistor without any problem.
Value of that offset resistor depend on type of probe (NTC or PTC, it is usualy PTC) and its T/R relationship.
It is certainly that 1ohm wont do the job.

Thermatech
25-02-2009, 08:10 AM
The min 19 is standard for all CM indoor units no matter which controls are being used.
There is a little known option for some indoor units for a 14 min but suggest get advise from ME technical before you proceed with this option.

dcool
26-02-2009, 06:00 AM
hi thanks for your help everyone went there yesterday and added a 57kohm resister inline to my return termister. Rooms where reading about 17 ,18 C display temp jumped to 21C :D set temp to 17 C cooling and rooms dropped to 14/15 C happy days......

dcool
26-02-2009, 06:06 AM
hi thanks for your help everyone went there yesterday and added a 57kohm resister inline to my return termister. Rooms where reading about 17 ,18 C display temp jumped to 21C :D set temp to 17 C cooling and rooms dropped to 14/15 C happy days......
just in case had the units set for 17 heating when i got there not much cooling needed in ireland this time of year......

nike123
26-02-2009, 07:01 AM
Be prepared that antifrost function now will not work properly.

nike123
26-02-2009, 07:02 AM
Ignore this previous post, something mixed in my head!:D

dcool
28-02-2009, 07:06 AM
nick what ya trying to do to me give me a heart attack :D:D that costumer is 3 hours drive from my workshop thought i was going to have to run down there...

nike123
28-02-2009, 08:10 AM
nick what ya trying to do to me give me a heart attack :D:D that costumer is 3 hours drive from my workshop thought i was going to have to run down there...
Yep, that is usually how I affect at peoples (they are few heart beats next to heart attack with my "bringing bad news skills"). :D;)