Hi everybody this is my first posting
Can you help me with a TK sea container that will not control at set point +4
The liquid line solenoid will not shut power to it all the time if you remove the coil the unit pumps itself down but will not cut out on Lp
Does this make sense?
It has i think two faults?

Brian_UK
21-02-2009, 10:10 PM
Sounds like the LP is setw rong or has been linked out.

richardb14
22-02-2009, 11:37 AM
maybe the solenoid has also been bypassed and its running straight from the stat

SKOOBY
22-02-2009, 08:35 PM
Do you know the exact model of the unit.

utc/tk foreman
24-02-2009, 01:45 AM
it could be the lpco is bypassed already, but the exact model number would help us all out.

teguh
27-02-2009, 06:52 AM
I think, you should check 24v power output from MRB ( for MP3000 ) to coil first.
It seems LPCO jumped.

Andy Longhurst
06-06-2009, 12:33 PM
Do you know the exact model of the unit.
Hi guys sorry foR the long delay in replying but have been very busy
the container is a CF11 M19.7
the unit will not control at set point +4 unit pumps itself down but will not cut out on lp no voltage coming out of the mirco p i have changed the lp last year what is the next step?