Is there a way to clear a blocked fridge capillary tube?

Thanks

nike123
21-02-2009, 07:41 AM
Easiest (and safest) is to change it together with filter-dryer!
There are some hydraulic pumps for cleaning capillary tubes. You clean them by pumping oil thru them with high pressure.
But you still need to de-braze them. Since you de-brazed them, it is easier to change them, then mess with pumping.

330i
21-02-2009, 09:34 AM
Thanks for you advice, it’s always of great help.
The problem is with this new fridges, they are so sealed, no way to get to the pipes, ai..

raz5
21-02-2009, 10:38 AM
The worst ones are when they are situated inside the suction line. Manufacturing a new suction line with the capillary inside is a nightmare. But as stated change the drier as well.

1torr
21-02-2009, 08:02 PM
I've used abs pipe cleaner in the past. Braze a bigger piece of pipe on the end of your capillary(5/8 or something) and use it like a funnel, blow it out with ofn into a container. Keep doing it until it comes out clean. Regards Kev.

Grizzly
22-02-2009, 10:12 AM
When would you feel it necessary to have to go to all that effort Kev?

Just wondered!
Steve

330i
22-02-2009, 02:40 PM
Thanks for all your replys,will try them

1torr
22-02-2009, 07:17 PM
Hi Steve, when you are called out at ten o clock at night to Bodmin to get the chiller working on a clients wire eroder. He loses 5k an hour else. Cheers Kev.

brian m w
24-02-2009, 12:27 PM
One thing we used to do was heat the back of the fridge up with a wall paper steamer, this helps the blockage in around 50% of the time as we used to do a lot of Beko's and they was a bugger for it.

Brian

amitsaxena
05-03-2009, 10:46 AM
Dear, I am having the experience to solve this .
1.Please cut the capillary at drier joint and Flush the system with Nitrogen, vaccum it and reachrge it. The problem will be solved.

2. Heat all the joint e.g. Capillary drier and drier condenser, and evaporator capillary. 80% problem will get solved for sure

nike123
05-03-2009, 11:07 AM
2. Heat all the joint e.g. Capillary drier and drier condenser, and evaporator capillary. 80% problem will get solved for sure

And 80% reoccurred again in short time!

amitsaxena
05-03-2009, 01:28 PM
Dear nike 123, you are write but not 100%, Your answer is ok, when it is related to cond joint.
Thanks

nike123
05-03-2009, 01:40 PM
Ignore, double post!

nike123
05-03-2009, 02:01 PM
Dear nike 123, you are write but not 100%, Your answer is ok, when it is related to cond joint.
Thanks


By heating drier you releasing captured water in dryer.
By heating joints you melting ice to moisture which circulate in circuit until it reach dryer. If dryer is saturated, than that moisture will form ice and eventually make restriction again.
And I did not even touched problem of acid formation because of free moisture in circuit.

Heating joint could only show to you, is the problem moisture or some other thing, what cause blocking. It is not solution of problem, if dryer is saturated.
I don't see any other reason (other than ice melting ) for joints heating.

frostedflake
24-03-2009, 11:25 PM
i'm not sugesting you do this, but once i saw a system that froze at the begining of the capilary tube and it was not working properly, the system had no service valve so what i did was to tap the begining of the capilary tube and then it suddenly stopped freezing and things went back to OK,

i know that whatever was blocking the cap tube is now a system contaminant flowing all over the system, but since this was a factory problem because no service valve was installed, and the unit is still working ok after 7 years i thought i'd share it with the forum.

regards

Gerhardt
29-04-2009, 02:06 PM
Hi 330i

from where in the north cape are you