Jonog
19-02-2009, 10:00 AM
Having a problem with fault 701, hot gas thermostat contact open having trouble finding the cause. Does anyone have a wiring diagram?

Brian_UK
19-02-2009, 07:12 PM
HI, according to the Prodialog codes, 701 is a high discharge gas temperature fault.

Which probably means you either have a faulty probe or you are short of gas.

The probe is in the compressor head.

Control manual here if wanted

http://eto.carrier.com/litterature/cm/13411.pdf

Full set of manuals for the chiller

http://eto.carrier.com/lit.asp


Scroll down to your model and 'search'.

nike123
19-02-2009, 07:58 PM
http://eto.carrier.com/lit.asp (http://eto.carrier.com/prodinfo.asp)



This link doesnt goes where it should be!
I think this is Ok link:
http://eto.carrier.com/lit.asp

Brian_UK
19-02-2009, 08:15 PM
This link doesnt goes where it should be!
I think this is Ok link:
http://eto.carrier.com/lit.asp

Thanks Nike, I had used an incorrect link earlier and then did a copy/paste. Somehow the original stayed underneath the link. :(

I've changed it now. ;)

absrbrtek
20-02-2009, 02:03 AM
Could be a nuisance trip if everything else is in order. Carrier had issues with the DTS years ago. It is on a dry circuit. You ohm it out and it reads good, but the board does not see it as closed. Carrier tech support had me jump them out as they felt the breakers and HP control would protect the compressor and the DTS wasnt needed. Just food for thought here.

fafa
23-02-2009, 10:18 PM
Hi,
I don't speak english very well. Excuse me
The DGT cut off near 115°C. Check the SDT.
If you don't read this temp, you have 2 solutions
1/ replace the dgt
2/check the starter guard board (put a jump)

If you read SDT near 100°C
Check the compressor.

Jonog
25-02-2009, 07:23 PM
Thanks for your help guys turned out that the jump on the board for B3 had a loose connection...

Brian_UK
25-02-2009, 07:45 PM
Thanks for the update and pleased to read that it was an easy/simple cure.