17-02-2009, 09:46 PM
HI ALL ANY ADVICE ?

Seem to have blockage on system have discharge pressure of 80 psi low and high pressure going into vacuum freezing out of lev from gauze. Have taken of lev and surrounding pipes cant find blockage all this after compressor failure. also have same problem on another mitsubisji system. found some sludge in the gauze near lev but nothing exciting any suggestions :cool:

Brian_UK
17-02-2009, 11:58 PM
Have you checked for any gauze at the evaporator connection.

laf100
18-02-2009, 12:06 AM
From memory there is a gauze strainer within/before the distributor "cone" -on Mitsu' cassettes anyway. I had one block many years ago on an R22 split with a long pipe run- obvioulsy no OFN purging during install by our subbies!:rolleyes: