vinod
12-02-2009, 02:02 PM
Hi,

I have chiller 30 gk (carrier) showing 17 fault alarm (cofiguration block fault). can some body help me to find out the problem?

narkom
12-02-2009, 04:58 PM
17 fault alarm is the oil pressure probe error comp. B1

vinod
12-02-2009, 08:39 PM
Hi,

it is xx17 fault (configuration fault-217)

Brian_UK
12-02-2009, 08:41 PM
It seems that you need to check the controls configuration.

Gibbo
12-02-2009, 11:53 PM
Assuming its the original RCPM board then its likely to be a faulty compressor protection module (RCPM). However check the LED'S are flashing Red which is power and Green which is the comms. If you have the controls book check the RCPM has the correct address (dip switches 1-8) see controls book for correct settings, if everything appears ok change board. You will need to set the dip switches on new board as per the old board, this then corresponds to the correct compressor.

vinod
15-02-2009, 02:55 PM
hi
I have checked the manual the DIP Switch position is correct and both LED,s Flashing. Both A1,B1 compressor's working A2,B2 is not running (code-217-cofiguration Block)

Gibbo
15-02-2009, 09:21 PM
Code 217 only applies to A2 Compressor RCPM board being faulty .
You will need to probably change the RCPM board for that compressor. Don't know why B2 Compressor is not running.

vinod
16-02-2009, 02:15 PM
In RCPM board there is MTA (8nos-DIP)
any changes of this switch will prevent the start the compressor? what will be the position of this.(30gk-100) 4nos compressor.

Gibbo
18-02-2009, 08:23 PM
The dip switches must correspond to the those listed in the control manual for each compressor otherwise their is a loss of comms between RCPM and Master Board.
Have you checked dip switches againest what is in the controls manual ?
Should you have to change dip switch settings ensure you switch off mains power to chiller.

vinod
19-02-2009, 03:37 PM
DIP Switchs are set as what mentioned
in control manual.(board adress).but MTA (DIP Switch)i don't find any settings in manual.

fafa
23-02-2009, 10:03 PM
Hi Guys,

I don't speak english very well ,so excuse me.
There's 2 gen of 30GK
Do you have the model and the serial number of it.
I will check tomorow

vinod
06-03-2009, 06:34 AM
hi guys

I started the chiller . MTA DIP SWITCH Was the trouble(settings) thanks for u r replys.

regards

vinod

Brian_UK
06-03-2009, 06:48 PM
Thanks for the update Vinod.