View Full Version : ua daikin fault



tait71
10-02-2009, 09:08 PM
hi chaps, i have a problem with a twin daikin system, one of my collages has replaced an outdoor pcb on a ry71gz7w1 3ph r407 outdoor now the system has faulted up a ua code (too many fan coils) i have set it up for a twin system with the controller setting 11, 0.02 i dont have any info on the outdoor board but have been told all the bit switches were set the same as the old one. any idears? tyred to ring daikin at 4.45pm uk time but got no answer :mad:

sorry the indoor units are fhyc35kzv1 x2

Brian_UK
10-02-2009, 11:08 PM
Try the SKy Air manual from the Daikin site.

You need file ESIE99-01 Series G

tait71
11-02-2009, 12:04 AM
thanks brian

nicolacozma
11-02-2009, 09:22 AM
Is happened before to receive an spare part PCB that has an software for another type of refrigerant. In that case you will have the same error UA. For Sky unit, from the outdoor dip-switches you don`t have the possibility to set the type of refrigerant (like for VRV outdoor PCB).

tait71
11-02-2009, 05:09 PM
been back today setup code 11 and 21 on the controller to twin setting, disconnected a condensate pump from indoor connections 1 and 3 (l and n) on marster, system running ok reconnected pump still ok, i just dont know? as far as i can tell the outdoor pcb is pre set for 407 and the only bit switches are for the defrost and emergency run but i stand to be corrected, thanks for help people:D

brunstar
15-02-2009, 10:41 PM
the reason this is happening is because you may have a link between the two fan coils on p1 and p2 and this must be removed as there should only be the p1 and p2 connected on the master unit