View Full Version : How do you determine type of refrigerant in the system?
tomtom
09-02-2009, 05:49 PM
Does anyone know how you are able to determine the type of refrigerant that is already inside the system? Sometimes the type of refrigerant that is actually inside the system is not the actual type that is specified on the unit's tag. Is there any way to tell what has actually been used in the system?:eek:
Any advice is appreciated. Thanks.
Thermatech
09-02-2009, 06:36 PM
Try taking the standing pressure of the refrigerant in the system & ambient temperature.
Look on a refrigerant comparitor to see which refrigerant has pressure which is a match for the temp.
Provided the system still has some liquid refrigerant this basic test should give first indication.
Quality
09-02-2009, 07:35 PM
look on TEV if fitted ,look at compressor lable for ref type or drier ,if its worth it get a sample analized
Plank!
09-02-2009, 08:05 PM
look on TEV if fitted ,look at compressor lable for ref type or drier
I see you've never worked on a "greencool" chiller.
Every component says R22 - they contain PROPANE.
Keep clicking yer pen top :rolleyes:
Quality
09-02-2009, 08:08 PM
i have not I take the hint:p
Brian_UK
09-02-2009, 08:13 PM
The only way to be sure is to get the refrigerant analysed or use a refractometer.
Quality
09-02-2009, 08:16 PM
The only way to be sure is to get the refrigerant analysed or use a refractometer.
ok another sarcastic remark:D
Brian_UK
09-02-2009, 08:18 PM
ok another sarcastic remark:DNot really, but if you read the OP you will realise that your answer does not relate to it. ;)
Quality
09-02-2009, 08:35 PM
words eaten or something like that ,oil and what has been:o
taz24
09-02-2009, 10:50 PM
.
Just check all the empty cylinders that will be dumped in the plantroom. :p
taz.
.
WINJA
10-02-2009, 08:20 AM
I see you've never worked on a "greencool" chiller.
Every component says R22 - they contain PROPANE.
Keep clicking yer pen top :rolleyes:
Did you say test flamability???:o
Hi! I know of an analyser under the barndname TASCO which is designed to determine the refrigerant compositions. The machine can even identify most HFC and even CFCs.
Hope it helps!
Regards
Koh - S'pore