31-01-2009, 09:26 PM
HI all of you
I have on York Air cooled chiller those data.
OIL pressure 18.5 barg -- OIL temperature 60.82 C
SP 5.32barg --ST 9.9 C
DP20.2barg --DT78.8
SAT SUC 9.1
SH 0.4
SAT DISCH 52.3
DISH SH 29.5
AMBIENT T 30
Leaving Water T 7.9
Retuern Water T 93.7
STEP 75
With a Laser thermometer i have on
The liquid line 32 C and afetr the economizer tthe liquid line is 12 C going to TXV .Before entrying the TXV , liquid line is 14 C , sight glass bubbling .TXV is iceing.
I have 43 C (1699KPA) at entrying of the dryer
Here is my conclusion
I have too subcooling and highdischarge pressure .
Super heat too small
for me there is to much refrigerant is the system .
Ive try to explain the Ice on TXV and Bubble on the sigthglass by the fact thtat the liguid line entryig the TXV too cool and surely the economizer( heat exhanger) should be full of liquid refrigerant.
Someone has try too set the TXV super-heat(I ve put back to the factory setting )but no change .
Was this troubleshooting correct.
PS It is R407C -Screw type chiller
I have on York Air cooled chiller those data.
OIL pressure 18.5 barg -- OIL temperature 60.82 C
SP 5.32barg --ST 9.9 C
DP20.2barg --DT78.8
SAT SUC 9.1
SH 0.4
SAT DISCH 52.3
DISH SH 29.5
AMBIENT T 30
Leaving Water T 7.9
Retuern Water T 93.7
STEP 75
With a Laser thermometer i have on
The liquid line 32 C and afetr the economizer tthe liquid line is 12 C going to TXV .Before entrying the TXV , liquid line is 14 C , sight glass bubbling .TXV is iceing.
I have 43 C (1699KPA) at entrying of the dryer
Here is my conclusion
I have too subcooling and highdischarge pressure .
Super heat too small
for me there is to much refrigerant is the system .
Ive try to explain the Ice on TXV and Bubble on the sigthglass by the fact thtat the liguid line entryig the TXV too cool and surely the economizer( heat exhanger) should be full of liquid refrigerant.
Someone has try too set the TXV super-heat(I ve put back to the factory setting )but no change .
Was this troubleshooting correct.
PS It is R407C -Screw type chiller