29-01-2009, 07:45 PM
I have one case where on compressor discharge has mounted anti vibration pipe which has leaked refrigerant out after only few days of operation.
Only data on pipe is HTH 37-08.
Does anyone know who is manufacturer of these anti vibrators.

What is correct term for them to search for manufacturers and their technical details? I forgotten English term for them. I think that we here use term "vibroflex"

Used refrigerant here is R410A and I fear that used anti vibrator is not strong enough for R410A pressures.
Unit is new one on the market. It is Galletti air to water heat pump MPE 028HO which is their first medium size system at R410A refrigerant.

Here is partial picture of anti vibration pipe.
http://farm4.static.flickr.com/3356/3236543411_916285ba68_b_d.jpg

dsp
29-01-2009, 08:17 PM
Hi Nike,
I just copied this form a catalogue I have. Down here we just call them vibration eliminators. The burst pressure is 500 psi on the one's I use.

VIBRATION ELIMINATORS
PIERCING & LINE TAP VALVES
SUITABLE FOR ALL HFC/HCFC/CFC REFRIGERANTS (Not ammonia)

Maximum Test Pressure: 1-1/2 times Operating Pressure shown above.
Minimum Burst Pressure: 5 times Operating Pressure shown above.
• Vibration eliminators are used in the suction and discharge lines of refrigeration and air conditioning systems.
• They are most effective when installed as close as possible to the compressor, preferably in a horizontal position (but
not essential), with the refrigerant line anchored at the furthest end from the source of vibration.
• Care should be taken to ensure that the vibration eliminator is not under static tension after soldering in place. They are
not designed to compensate for lines that are out of alignment, so make sure lines are straight and in in line.
• High temperature alloys


Hope this helps.
dsp

nike123
29-01-2009, 09:34 PM
Hi Nike,
I just copied this form a catalogue I have. Down here we just call them vibration eliminators. The burst pressure is 500 psi on the one's I use.

VIBRATION ELIMINATORS
PIERCING & LINE TAP VALVES
SUITABLE FOR ALL HFC/HCFC/CFC REFRIGERANTS (Not ammonia)

Maximum Test Pressure: 1-1/2 times Operating Pressure shown above.
Minimum Burst Pressure: 5 times Operating Pressure shown above.
• Vibration eliminators are used in the suction and discharge lines of refrigeration and air conditioning systems.
• They are most effective when installed as close as possible to the compressor, preferably in a horizontal position (but
not essential), with the refrigerant line anchored at the furthest end from the source of vibration.
• Care should be taken to ensure that the vibration eliminator is not under static tension after soldering in place. They are
not designed to compensate for lines that are out of alignment, so make sure lines are straight and in in line.
• High temperature alloys


Hope this helps.
dsp



Thanks dsp!
Do you have manufacturer name of that vibration eliminators?

nike123
29-01-2009, 09:37 PM
Does anyone have any names of vibration eliminators manufacturers in Italy or in EU?

I found:
Carly

http://www.vibrasorbers.com/

These Chinese is only 35 bar rated (500psig):
http://cntw.en.alibaba.com/product/206275421-200189967/vibration_absorber.html

These are only 28 bars rated (fi 22)
http://www.amnitec.nl/UserFiles/File/Vibes.pdf

Toosh
30-01-2009, 03:47 AM
Does anyone have any names of vibration eliminators manufacturers in Italy or in EU?

I found:
Carly

http://www.vibrasorbers.com/

These Chinese is only 35 bar rated (500psig):
http://cntw.en.alibaba.com/product/206275421-200189967/vibration_absorber.html

These are only 28 bars rated (fi 22)
http://www.amnitec.nl/UserFiles/File/Vibes.pdf

Hi Nike I always used Anaconda

http://www.universalmetalhose.com/products/spec_vibration.htm

Regards Norm :D

Sorry I posted the same post twice

nike123
30-01-2009, 07:42 AM
Hi Nike I always used Anaconda

http://www.universalmetalhose.com/products/spec_vibration.htm

Regards Norm :D

Sorry I posted the same post twice


They are no good, for fi22 maximum operating pressure is 30 bar.
On high side I normally have 30-35 bar.

Toosh
30-01-2009, 07:57 AM
Hi Nike, I have found anaconda failure in stressed piping, meaning the pipe has been been cut to short and pulled into fit which creates stress, and most products are usually have a failure point well above the operating pressure

Norm

nike123
30-01-2009, 04:37 PM
Hi Nike, I have found anaconda failure in stressed piping, meaning the pipe has been been cut to short and pulled into fit which creates stress, and most products are usually have a failure point well above the operating pressure

Norm
Could be the case here, but I still want to find equipement rated for higher operation pressure.

US Iceman
30-01-2009, 05:08 PM
You might try some suppliers of hydraulic hoses and fittings. The pressures and fluids they work with could provide a reasonable option for you.

nike123
30-01-2009, 05:22 PM
You might try some suppliers of hydraulic hoses and fittings. The pressures and fluids they work with could provide a reasonable option for you.

I am more leaned toward fitting plain annealed copper pipe in place of this vibration eliminator bended to compensate for this vibrations

superswill
30-01-2009, 08:19 PM
nike

do you have the space to replace the anti vibration pipe with a small coil shaped piece copper piper? i have had this problem on an old airdale package and made up a loop the loop arrangement of 5/8th and fitted that in its place,ok it it would not win a beauty pageant but it has done the job

US Iceman
31-01-2009, 12:58 AM
I am more leaned toward fitting plain annealed copper pipe in place of this vibration eliminator bended to compensate for this vibrations

If the tubing is small enough for you to bend it into multiple loops, that might be OK. One thing to remember though... If the loop is vertical, it can trap oil or other in it during shutdown. If the loop is horizontal you can arrange it so the loop drains freely.

I have used some of the hydraulic hoses and connectors before and had good luck with them.

nike123
31-01-2009, 11:37 AM
If the tubing is small enough for you to bend it into multiple loops, that might be OK. One thing to remember though... If the loop is vertical, it can trap oil or other in it during shutdown. If the loop is horizontal you can arrange it so the loop drains freely.

I have used some of the hydraulic hoses and connectors before and had good luck with them.
I think that 3 U turns in different planes and arm of pipes in length of 30-40cm will be sufficient.
This should be the shape but without elbows ( pipe would be from one piece and bended in this shape).

http://farm4.static.flickr.com/3529/3240424219_e6699bf831_b_d.jpg

It is small scroll of 25 kW of refrigeration power and not much vibrations from what I seen first few days.
Maybe cause of vibration eliminator failing was fact that few days before failing unit was out of level some 3-5° because of unit anti vibration foots are fall out on one side of unit.

monkey spanners
31-01-2009, 12:11 PM
I think the pressure rating of vibration eliminators drops as the size increases. What size pipe is it used with?

Jon

nike123
31-01-2009, 12:24 PM
I think the pressure rating of vibration eliminators drops as the size increases. What size pipe is it used with?

Jon


22mm at discharge of compressor to the reversing valve.

chemi-cool
31-01-2009, 01:17 PM
Follow US iceman post,
I only use SS vibration eliminators from the hydraulic sector, they are made up to 400 Bar.

On the other hand, Why use VE on hermetic compressor?

nike123
31-01-2009, 01:45 PM
Follow US iceman post,
I only use SS vibration eliminators from the hydraulic sector, they are made up to 400 Bar.

I think it is too expensive and complicated to fit if there is no brazing connections at them. I also don't know where to find them here. Could you point me to some page where i could find more technical details and connection options?


On the other hand, Why use VE on hermetic compressor?

It appears that someone in construction department of this unit thinking that they are necessary. Although, they are not fitted at suction side.

US Iceman
31-01-2009, 03:40 PM
Most of the energy for vibration is in the discharge lines, so that makes sense if you want to prevent the vibration (or noise) from traveling.

3 changes in direction for the loops is typical of expansion loops for increased flexibility to prevent pipe rupture or failure due to temperature related growth or shrinking of pipes. However, I do not think this will do very much for reducing vibration.

The issue with vibration is; trying to prevent the mechanical vibrations from creating mechanical failures or transmitting noise.

chemi-cool
31-01-2009, 08:29 PM
Hi Nike,
I will try to get you some pictures of these VE soon.

About hermetic compressors, they are equipped with internal springs to absorb any vibrations. If you get any, check for broken valves.
Don't forget that hermetics turn RPM .
you can try to change the RST to TRS, keep the same rotation direction and some times it reduces the vibrations.

nike123
31-01-2009, 08:45 PM
Hi Nike,
I will try to get you some pictures of these VE soon.

About hermetic compressors, they are equipped with internal springs to absorb any vibrations. If you get any, check for broken valves.
Don't forget that hermetics turn RPM .
you can try to change the RST to TRS, keep the same rotation direction and some times it reduces the vibrations.

Thanks Chemi!
It is Maneurop Performer scroll SH120A4ALB and it is turning right way. And, as I said earlier, I don't think that it is his vibrations what is responsible that vibration eliminator failed.

nike123
31-01-2009, 08:55 PM
Most of the energy for vibration is in the discharge lines, so that makes sense if you want to prevent the vibration (or noise) from traveling.

3 changes in direction for the loops is typical of expansion loops for increased flexibility to prevent pipe rupture or failure due to temperature related growth or shrinking of pipes. However, I do not think this will do very much for reducing vibration.

The issue with vibration is; trying to prevent the mechanical vibrations from creating mechanical failures or transmitting noise.

When I was examining at initial start up of unit, I did not found that compressor makes any excessive vibrations or that vibration eliminator moves at all. In fact I found work of this compressor pretty smooth and quiet in comparison with earlier versions of Performers for R407C.

chillerman2006
31-01-2009, 09:04 PM
Thanks Chemi!
It is Maneurop Performer scroll SH120A4ALB and it is turning right way. And, as I said earlier, I don't think that it is his vibrations what is responsible that vibration eliminator failed.

Nike

i have had the same problem on new 410a units that were cracking the discharge pipe and it turned out to be cheap copper tubing - replaced with soft copper tubing with minor bend to take the movement at startup - job done - should be no need for vibrosorber:)

monkey spanners
31-01-2009, 09:34 PM
The Henry 7/8" 22mm vibration eliminators in my catalogue are rated at 34.5 bar, don't know what make yours was though.

sedgy
10-01-2011, 06:40 PM
hi all the correct metod of using anaconda,s is that they are used in pairs= one vertical and one horizontal close together so that all the movement is taken by the anaconda,
of corce the pipework must be fasened = no movement .
sedgy