Hi, I was chatting to a chap recently about charging a small freezer running on R404a with capillary expansion. He said he charges the system by putting the evaporator fan OFF and waiting for about an inch of frost past the evaporator outlet. The thermostat would obviously be on its lowest setting to put the unit on full load. I have heard of this before, but never tried it. Is it a trick of the trade? Can someone explain the theory about whats happening!
Another technician told me you can also use that method with an internally equalised txv. I pressume the bulb senses the S/H, lowers the pressure on the diaphram, thus the valve starts to throttle back, until all three pressures in the valve equalise. This frosting would then indicate that there is enough liquid in the evaporator. He said if no frost was present it would indicate that there is still too much vapour in the evaporator.
Thanks
Another technician told me you can also use that method with an internally equalised txv. I pressume the bulb senses the S/H, lowers the pressure on the diaphram, thus the valve starts to throttle back, until all three pressures in the valve equalise. This frosting would then indicate that there is enough liquid in the evaporator. He said if no frost was present it would indicate that there is still too much vapour in the evaporator.