View Full Version : moving 4 mitsi Elec G50 controllers



Enviro-Cooler
19-01-2009, 09:45 PM
Got to move 4x G50 controllers.
obviously means cutting power to them, is there battery backup or do they all need re programming?? :rolleyes:
First time working on mitsi elec stuff, any help?tips would be much appreciated.

Thermatech
20-01-2009, 06:28 PM
G50 central contollers have battery back up which should last weeks rather than days.

Provided you make no address setting changes to any indoor units or local remote controllers you can disconnect from the power pack & systems. Then reconnect at the new location. Power back up & all should be as before.

But if this is part of a refit of the building & other changes have been made to indoor units & indoor unit groups then some reprograming will be required to reflect the new systems setup.

Enviro-Cooler
20-01-2009, 08:07 PM
all`s staying as is with the indoor units.evreything should be fine then! thanks for the help