16-01-2009, 12:13 AM
Is it a legal requirement to have the amount of gas in each system recorded

Brian_UK
16-01-2009, 12:46 AM
Yes it is; and the type.

It should all be kept in the equipment register.

icecube51
16-01-2009, 04:24 PM
and the owner and the location and the last technician ho serviced the plant,....no???

Ice

multisync
16-01-2009, 05:34 PM
Yes it is; and the type.

It should all be kept in the equipment register.

A link please?

Brian_UK
16-01-2009, 08:18 PM
F Gas Regulations

superswill
16-01-2009, 08:27 PM
A link please?

please see:

http://www.acrib.org.uk/MG7PNL36445

hope this helps

multisync
17-01-2009, 12:29 AM
My understanding of the question was for each system ie every system irrespective of size,gas etc. F-gas relates to only those gases covered and only for systems above 3kg, which is why I asked for a link.



Is it a legal requirement to have the amount of gas in each system recorded

El Padre
17-01-2009, 01:51 AM
I agree, I have the misfortune of looking after a site with over a hundred versatemp units, and was informed then that the register only applies to systems 3kg and above.
I guess that we shall all find out when we sit the new safe handling exams!!

pentond1
24-01-2009, 01:17 PM
Is there a chart for pipesize- length - bends to allow me to calculate the weight Kg of gas in pipework.

nike123
24-01-2009, 01:39 PM
Is there a chart for pipesize- length - bends to allow me to calculate the weight Kg of gas in pipework.
Don't you think that gas weight depend on density, which depends on temperature. And, what with mixture of gas and liquid in pipe?

You could use Coolpack software for calculation of liquid and gas flow in pipes and fittings! From that you could estimate/calculate weight.

pentond1
24-01-2009, 02:27 PM
To enable the calculation of weight Kg in pipework (R407C) to be added to the condenser - compresser. Is there not a chart giving the weight for various diameters of pipes listing the kg/m in a liquid line.

nike123
24-01-2009, 03:03 PM
To enable the calculation of weight Kg in pipework (R407C) to be added to the condenser - compresser. Is there not a chart giving the weight for various diameters of pipes listing the kg/m in a liquid line.


If you have Excel, it is easily calculated from pipe dimensions and density.

Tables you could find here at page 11:

http://www.suva.dupont.ca/pdf/RefrigPipingHandbook.pdf

pentond1
24-01-2009, 03:05 PM
Found information on manufacturers website giving pipe size curves and the Kg /m required

pentond1
24-01-2009, 03:13 PM
Many thank for you help nike123

Peter_1
25-01-2009, 08:49 AM
and the owner and the location and the last technician ho serviced the plant,....no???

Ice

And even more, corrective actions you've taken to prevent a new leak.
And... a compulsory second control within a month to verify if your repair was OK.

Peter_1
25-01-2009, 08:53 AM
I agree, I have the misfortune of looking after a site with over a hundred versatemp units, and was informed then that the register only applies to systems 3kg and above.
I guess that we shall all find out when we sit the new safe handling exams!!

That's correct and 6 kg and above for factory hermetic made units (like monoblocs, chillers,...).
I'm a jury member and chairman of the Jury in th Dutch speaking part of Belgium, so if you have questions...
You can find everything you need to know in the new EN378-2008.

multisync
25-01-2009, 10:49 AM
And... a compulsory second control within a month to verify if your repair was OK.

I was of the understanding that this part was/is dropped as not being viable?

If not or it is not going to be dropped what is meant by-


If a leak is detected and repaired, a further check must be carried out within one month to ensure that the repair has been effective

Peter_1
25-01-2009, 11:04 AM
Link: EN378-4:2008, Appendix D. - D5

Translated from Dutch: The applications must be controlled on leakage within 1 month after repair of the leak to ensure that initial repair was effective.

Greengrocer
29-01-2009, 07:16 PM
To enable the calculation of weight Kg in pipework (R407C) to be added to the condenser - compresser. Is there not a chart giving the weight for various diameters of pipes listing the kg/m in a liquid line.


Take a look at this calculator / spreadsheet off the Defra website.

www.defra.gov.uk/environment/air-atmos/fgas/comply/quantity.htm

nike123
29-01-2009, 08:50 PM
Take a look at this calculator / spreadsheet off the Defra website.

www.defra.gov.uk/environment/air-atmos/fgas/comply/quantity.htm (http://www.defra.gov.uk/environment/air-atmos/fgas/comply/quantity.htm)

I have done calculation with this spreadsheet on one chiller and calculated minimum is 12kg and max 20kg.
System actualy have 7,5kg of refrigerant.:eek: